Bespoke Inspection Chamber?


dnoble

Recommended Posts

I have a long (55m) run from house to mains sewer in road 

We laid 110mm pipes with appropriate drops (for  foul and surface/roof water) next to each other in trench. 

Building inspector checked and said fine. 

Called next day and said " by the way you need an inspection chamber every 22m" (therefore 2 and need to include both pipes).

This is going to be very fiddly to retrofit (builder hadn't done a run this far before and didn't know of this rule)

Also inspection chambers all seem to have radial pipe entrance. 
I need one 300-500mm accross with 2 parallel pipes in the bottom. 

I cant find such a thing online. 

Is the only option building one out of blocks or something??

 

Link to comment
Share on other sites

A quick search seems to throw up several with opposing inlet/outlets:

 

https://www.plasticdrainage.co.uk/cs320-inspection-manhole-chamber-set.html

 

https://www.drainagepipe.co.uk/products/complete-inspection-chamber-sets/300mm-mini-inspection-chamber-complete-set-unique/300mm-mini-inspection-chamber-complete-set/

 

maybe two of the smaller ones can be set side,by side, offset down the run by a metre?

Link to comment
Share on other sites

I understood that it was 45m between inspection chambers. I also think you could just put a rodding eye for the foul and not bother with the surface water. Ask Marley or Polypipe technical for backup if required. Easier to send them a drawing than mess with digging up drains.

Link to comment
Share on other sites

Hi Jeremy, thanks. That last one looks like a possibility if they are building regs passable. Yes otherwise the offset option squeezed in might work, though you'd have to chop a bit out to accommodate the uninspected pipe

Link to comment
Share on other sites

23 minutes ago, Mr Punter said:

I understood that it was 45m between inspection chambers. I also think you could just put a rodding eye for the foul and not bother with the surface water. Ask Marley or Polypipe technical for backup if required. Easier to send them a drawing than mess with digging up drains.

I agree - I am pretty sure 45m from IC to IC.  Table 13 of Part H.

Link to comment
Share on other sites

Th ebuilding insepctor was pretty clear you needed one for any run over 22m. 

Could you provide a link? I've just looked at table 13 part H it isn't very obvious what applies to me. It mentions 22 and 45m 

 

https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/442889/BR_PDF_AD_H_2015.pdf

Link to comment
Share on other sites

1 hour ago, dnoble said:

Th ebuilding insepctor was pretty clear you needed one for any run over 22m. 

Could you provide a link? I've just looked at table 13 part H it isn't very obvious what applies to me. It mentions 22 and 45m 

 

https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/442889/BR_PDF_AD_H_2015.pdf

On the left hand side of that table you have a list of various access points....along the top you have the lost of 'to' access points.

 

So....inspection chamber shallow 'to' inspection chamber is 45m.

 

Not trying to be patronising...thats how I read the table.  Maybe others read it differently?

 

I'm not sure how IC to IC is ever 22m?