Yesterday at 19:551 day I want to avoid having eaves and have come up with a proposal for how I could potentially achieve a minimalist guttering design and one where the down pipe runs straight down with everything being in the same vertical plane. The only thing I want to check is the proposed airflow route and possible condensation risks of doing it this way. I plan on running a custom flashing with a drip edge underneath the guttering to ensure there is no rain water ingress.
10 hours ago10 hr Two things to considerExtend the custom metal flashing up and round the edge of the slope to fully protect under that drip "edge".Before fitting the custom flashing apply some form of waterproofing for belt and braces protection.Assuming those a vertical battens behind your horizontal ones, the airflow seems good
5 hours ago5 hr Do not adopt this approach! The amount of roof void ventilation may be insufficient. More importantly there is the fire risk as any fire and/or smoke can travel, unseen, from the wall to the roof space. The Building Regs cover this in Approved Doc B - the 2 cavities should not connect, a cavity barrier should be installed at the top of the wall cavity.
5 hours ago5 hr I am with @ADLIan . You need a fire stop between the top of the wall ventilation and the start of the roof.
28 minutes ago28 min Author Ok. I wasn't sure whether a fire stop was required in the wall cavity if you have used full fill mineral wool cavity batts?Regarding the ventilation concern I can add an over fascia vent.I assume the void behind the cladding has to be able to vent somewhere, or does it not?This could be wrong, but a quick AI search.Why Fire Barriers Are ExemptNon-combustible full-fill exception. Under UK Building Regulations (Approved Document B), cavity barriers are not required in external masonry walls if the cavity is totally filled with non-combustible insulation. DriTherm 32 is glass mineral wool with the highest Euroclass A1 fire rating.Wall construction conditions. To qualify for this exemption under Approved Document B, the inner and outer masonry leaves must each be at least 75mm thick, and the slabs must tightly fill the entire cavity with no air gaps.Height limits. According to BBA Agrément Certificate 95/3212, DriTherm 32 is approved for use in buildings up to 25m high, though additional fire and detailing checks apply to buildings over 11m or 12m. Edited 8 minutes ago8 min by flanagaj Added AI thoughts
Just now1 min That may be the case with the full fill insulation between the brick and the block but you have created another ventilated cavity in the wall that links with the roof cavity. Please read AD B.