19 hours ago19 hr I want to avoid having eaves and have come up with a proposal for how I could potentially achieve a minimalist guttering design and one where the down pipe runs straight down with everything being in the same vertical plane. The only thing I want to check is the proposed airflow route and possible condensation risks of doing it this way. I plan on running a custom flashing with a drip edge underneath the guttering to ensure there is no rain water ingress.
5 hours ago5 hr Two things to considerExtend the custom metal flashing up and round the edge of the slope to fully protect under that drip "edge".Before fitting the custom flashing apply some form of waterproofing for belt and braces protection.Assuming those a vertical battens behind your horizontal ones, the airflow seems good
15 minutes ago15 min Do not adopt this approach! The amount of roof void ventilation may be insufficient. More importantly there is the fire risk as any fire and/or smoke can travel, unseen, from the wall to the roof space. The Building Regs cover this in Approved Doc B - the 2 cavities should not connect, a cavity barrier should be installed at the top of the wall cavity.
Just now1 min I am with @ADLIan . You need a fire stop between the top of the wall ventilation and the start of the roof.