Tepid Tiles I Am Mystified

Featured Replies

  • Author
On 09/11/2026 at 14:04, JohnMo said:

I would take out to middle position see how everything responds, if still not meeting temperature expectations, screw it another turn etc.

Yesterday, the response to fully opening the flow regulator was encouraging. The temperature increased to 40 degrees. The ufh temp stayed at 38- 40 for the rest of the day and it was at 38 degrees at 06.00 this morning. There was a discernable, though small increase in tile temperature.

However, the flow rate had dropped from 1.5 to 1.0. I changed the pump setting from one to two which gave a drop in flow rate. Since then, with the pump set at two, the water temperature has dropped to 34 and now 24 (despite the boiler still having 40 degree water available and heating the radiators efficiently).

The flow rate is now sitting below 0.5 and water temp at 23 degrees.

On 09/11/2026 at 14:04, JohnMo said:

I would take out to middle position see how everything responds, if still not meeting temperature expectations, screw it another turn etc.

20261111_075834.jpg

  • Replies 52
  • Views 727
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • Nickfromwales
    Nickfromwales

    No, it is not a bleed / vent. It is an isolation valve aimed at commissioning the flow rate of water through the system. It is basically an Allen key operated gate valve. The T off at the very top of

  • If the OP has screwed this fully closed, he will get no water or maybe very little water leaving and therefore entering the system, and a flow temp cooler than expected, which is what they are seeing.

  • Is the room up to temperature? And how how have you given it to heat up? UFH doesn't or shouldn't have a hot floor. 32 degs is below body temperature so it will only feel tempid.

Posted Images

  • Author

At midday it has settled at 30 - 32 degrees with the flow remaining just shy of 1.

I don't understand why adjusting the pump rate had a retrograde effect on the ufh water temperature. Does it indicate component fault?

20261111_121821.jpg

20261111_121907.jpg

For a long term, effective and robust solution, I’d change the pump and mixing valve arrangement. This one is very crude, and looks to be quite an old setup too.

These are what I fit if I need a mixing valve:

image.png

Note the position of the thermo control head. The boiler can pump to this and bypass back, vs the flow being strangled off.

Also you’ll gain the modulating pump which will adapt to the required duty.

One other thing to rule out is air-locked UFH loops. Was the system flushed or purged through ever?

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.