Ecodan r32 keeps flipping into immersion mode.
Morning hive mind - really hope you can help.
We have a Ecodan r32 installed about 3 years ago. Not long after, it would occasionally flip into immersion mode and need restarting. Since then it has gradually got worse and is now happening every day or two. Some details
- no faults showing
- legionella mode set to 30 days
- Heating is auto adaptive mode
- House has rads upstairs, UFH down
- Stats run through wireless UH8-RF V2
- Seems worse when stats are calling for heat. When all stats are off then it doesn't happen so often
- immersion mode doesn't seem to heat the water either - only around 18 degrees
We've spent hundreds on not getting it fixed so need a different route! Original installers not very helpful; charge for call out but don't fix issues. We have a decent freelancer who does the annual service but he doesn't seem able to fix it either.
My wife is now threatening to take the kids to live in a hotter country (again).
It has to be a basic setting messed up.
Let's go back to basics
Why is the immersion there - to provide additional heat when the heat pump isn't working or cannot provide enough energy heat the house.  It is activated based on timers based on getting temperature water flow temperature up to an expected level.
You can have the immersion heater modes set various ways and for various times.
I would get the manual out and have a good read, understand what is happening.  Post your settings on here - possibly your manual also.
Unless you have health reasons to use it, I wouldn't bother with mode - do a risk assessment - many available online.
Also are you talking about your heating or domestic hot water?
Thanks John.
Our Heat Pump does both heating and hot water but I'm not sure what immersion mode is trying to do when it kicks in. Maybe just supply the domestic hot water. Either way, it doesn't work as it never gets above 20°
I'll have a proper look through the settings and report back.
So if DHW and it's only getting to 20 degs good chance it is a time related issue.  Also check your diverter valve is moving from heating to hot water production.
So dig out all the DHW settings
Can you alter the hot water schedule to come on during the day when you can watch what happens when it tries to heat the hot water?
There Should be little need for space heating just now so I would focus on getting the hot water up and running. Do you know what the "stats" do as you shouldnt need them if running in auto adaptive mode.
If you're really under pressure to get this sorted I would contact any local Heat Geek engineers and see if they have Ecodan experience and can help out.
My reading of the OP is that the heating is still working (as a heat pump) but there are spurious activations of the immersion during which time the system doesn't heat up.
OP says "it doesn't heat the hot water either" so I assumed it's CH and DHW??
'In immersion mode' which it only sometimes switches to.
So my reading is that the system works fine for a while then something happens and it stops working as normal and needs resetting and then it works again.
@MorganP can hopefully confirm.
This is correct, thanks Rick. The heating and hot water work well when the ASHP is running. The issue is that the ASHP randomly cuts out and flips into immersion mode. Given that immersion mode never gets above 20 degrees, it's effectively useless at that point. It kicks back in after I restart the system. The installer annoyingly put the main controller in the garage next to the tank - always fun being out in my dressing gown first thing in the morning
So my Ecodan set up should (I think) have the water on permanently. It's set to heat to 50°. It then has a 10° drop off before kicking back in, and presumably going back up to 50. That seems correct because when it's working, the water is rarely below 40° according to the MelCloud (Mitsubishi) app. I'm not sure how to manually check the diverter valve but I'm pretty sure that's fine too as the heating works well when the ASHP is running.
Hmm, so very frustrating.
Is the immersion broken/ failed and when the heat pump goes to call it on (legionella?) it doesn’t heat up and trips out in fault?
Thanks again for the feedback. There's no fault showing but your point does flag two things that aren't necessarily related.
Firstly: I think the immersion may be faulty as it doesn't get over 20 degrees. I can't see a specific immersion temperature setting. I assume the Ecodan controller would try and use the immersion heater to get to the regular tank temp of 50°. If so then it's not working properly. If anyone knows how it's meant to work I'm all ears!
Secondly: Even if true, I can't see how the above issue wouldn't be the reason it trips into immersion mode in the first place.
@Dillsue - following this comment I'm trying to isolate the issue. For now I've switched off the heating all together on the controller. I did think that auto adaptive mode would use the stats though. There are three modes - fixed flow, compensation curve and auto adaptive. I assumed all three would still need the stats to call no?
Change one thing at a time but another thing you could try is to disable the legionaire cycle (I don't know the heatpump but I imagine it might be possible it has tried to use the immersion for that, detected some fault and got into a loop where it keeps retrying).
The 3 modes you mention can all likely run without a stat but your installer may still have put one or more in. Have you got multiple stats suggesting you've got zoned heating? This is unlikely to be relevant whilst you are trying to get the DHW sorted.
In your first post you say the system started with this issue soon after installation?? Did the installer not sort it out then, or try to??
The immersion may or may not be faulty but theres likely another fault as the HP should be able to heat the DHW way beyond 20 degrees without needing the immersion....there's no point in having the heat pump if it's going to default to using the immersion!
Yeah, the house has UFH, zoned with stats connected to a wireless UH8-RF V2 unit (attached). When the HP isn't tripped into immersion mode, the heating is fine. Zones call for heat, the HP kicks in etc.
I have the Heating switched off at the mo, and it hasn't cut out in a few days. I wonder if it's an issue specifically to do with the heating. Maybe the HP can't generate enough heat so calls for the immersion to kick in, and then everything cuts out. Does that sound likely? Water temp is set to 50° / auto adaptive.
Regarding original Installers. Hmm. Competent installers but abysmal aftercare. Very quick to charge (whether they fix your problem or not).
So with the immersion enabled for heating (CH) it will be looking for a time to reach target flow temperature, this likely to be adjustable setting within the controller.  If a lot of zones call for heat and your screed is cool, the time limit is possibly exceeded to get to target flow temperature.  The heat pump controller says I need assistance the heat loss is bigger than I can cope with or the heat pump is broken turn on immersion. This mode is likely to remain the whole time you are calling for heat it should reset when heat is satisfied.
A lot of the issue maybe as a result of how you operate the system, having lots of room thermostats are these all timed to go on and off a different periods during the day, or just set to a fixed target all day every day and acting as room limiters?
BUT - You need to clarify clearly is the 20 degs room temperature or cylinder temperature? Because to me it's not clear?
I assume the "50 degrees/auto adaptive" is 50 degree DHW set point and auto adaptive for the space heating(CH)??
So if it's not tripped for a few days, is the DHW up to 50 degrees and reheating as you use it ie things are normal??
Edited by Dillsue
I have an Ecodan R32. Have you checked the heat source setting via the service menu? The "Heat Source" should be set to "Standard". If it's set to "Heating" that's wrong and needs to be changed to "Standard"