I want to add some more PV panels to my system. The ones I have all face south with no shade
The panels I want to add will face east and west.
What sort of panels can if fit to the two separate rings I already have without losing power from the existing ones?
You just put the new one a different inverter or if your existing inverter has spare MPPT do that, then they can be anything you want.
East and west can go on one MPPT (but need to be same panel design, same number of panels and same angle) or 2x MPPT if you want.
Do not connect on the same MPPT as your existing South facing, as new panels are very unlikely to match your old ones
Edited by JohnMo
Hi @JohnMo
I will come back to this if you don't mind.
I need to change my inverter to one that will allow my system to charge batteries, supply to the mains, and go off grid. Is there such a thing?
Hybrid inverter. But they are generally equipped to do limited off grid output.
Some makes will do a gateway which will allow the full inverter output in a power cut.
Or AC coupled battery with gateway will will allow normal string inverters to work in a power cut. Depends if you already have your battery?
All the above depends on what you mean by off grid?
11 minutes ago, Marvin said:
Hi @JohnMo
I believe Tesla powerwalls do this, but it’s a hard thing to achieve in the UK as in the event of a power failure, any generation or potential export should turn off or island, and for that reason most don’t operate the whole fuseboard on backup, rather just a backup socket for emergency loads to be plugged into. Maybe someone else knows more about this, but mine certainly doesn’t as an AC coupled.
Don’t agree with East and West connecting to same MPPT, my east and west panels are both active in differing amounts simultaneously, and in winter east does far better than west.
Either use a separate inverter, or get a triple MPPT one to handle all 3 strings, these are widely available as normal and hybrid.
A good question, do you get the feed in tariff? If you do then don’t go hybrid, as it will wipe out a lot of your income.
I didn't until someone here pointed me towards design / install instructions that said you could, so researched further. And indead you can and the output per year is actually better than 2x MPPTs as they run longer at best efficiency point. But strings need to be identical, as in number of panels, mounting angle.
wonder how that comes about? Just can’t imagine it from my own install. Have you done this and observed the output difference?
Maybe Im missing something but the Fronious write up is comparing output of 2 E-W arrays each with different panels, mounted at differing inclinations and facing different directions?? Hard to see how you'd get a meaningful comparison of them wired to a single inverter VS 2 separate inverters??
Think your missing something. One of the rules is the east and west face panels have to be matched. They are comparing essentially 4 systems. One thin film, to one inverter and also 2 inverters, same for Crystalline.
Just re read it and understand how they've split the arrays....as you say.
I'm not sure how valid that paper is with today's kit. The paper seems to be from 2013 when panels were a fraction of the wattage/current than they are today. For a single inverter/MPPT system they say the E/W arrays must be wired in parallel which will significantly increase the current over that of a single E or W array. Back in 2013 the combined current would still be quite low and likely manageable by a single inverter/MPPT. With modern panels the current is significantly higher than those from 2013. Put 2 modern arrays in parallel and you could go over a single inverter/MPPT limit??
With figures plucked off the Web you've got a max 15A DC input for a solis 5kw inverter and Longi 450watt panels with a max 11A output. Put 2 longi strings in parallel and I'd be pretty sure your going to exceed the inverters 15A input limit??
Very true.
A 3x MPPT hybrid inverter may be a better solution. Assuming a DC battery. If AC coupled battery any 2x MPPT inverter in addition to the existing inverter would be fine. Just need to manage the export limit.
There are two ratings on an MPPT for current. One is the maximum current it can usefully convert, the other is the max short circuit current. As long as your arrays in parallel stay below the max short circuit current then the effect of having more generation capacity on one MPPT than it can handle just limits the maximum energy you can generate. On an East/West (or North/South) array it's very unlikely both sides will be operating near maximum at the same time and for the few hours per year they do its not necessarily worth the cost of another MPPT.
Solar panels are so cheap compared to everything else that it's often worth maxing them out to increase generation outside peak/during winter at the expense of not being able to use all generated energy in peak summer.