MrWhat Posted 2 hours ago Posted 2 hours ago Hi All, I am chatting to an engineer with regards to getting an ASHP via the MCS grant. He has recommended a 8kw Veissmann Vitocal 150-A heat pump and has told me that it will be necessary to have a buffer installed if i want to use the cooling function of the pump. Is anyone aware if this is the case? My underfloor heating capacity is 228 litres.
Dave Jones Posted 2 hours ago Posted 2 hours ago remove all zoning controls (if any fitted), 8kw sounds very large, what do the heat loss calcs say the engineer has provided to you backing up his design of 8kw being required ?
JohnMo Posted 2 hours ago Posted 2 hours ago Zero idea why you would need or want a buffer. Other comments as per @Dave Jones.
MrWhat Posted 1 hour ago Author Posted 1 hour ago I have no zoning. My heat loss calcs are showing worst case 5kw which was LoopCAD and as low as 3.9kw (1 air change per hour) 4.7kw (2 ACPH) using Jeremeys spreadsheet from this forum. Obviously air changes per hour are a guess at this stage . He has based this on the build information i have given him at the moment. He has said that the heat pump looses 25% efficiency on defrost cycle which is the reason for recommending the larger pump. Its a 5 bed 350m2 ICF build
JohnMo Posted 1 hour ago Posted 1 hour ago Our house sounds a similar build, we have lots lots glazing 192m² and we have 4kW heat pump. Your calculations sound in the right ballpark. Do not over size, you will take an efficiency hit. important to look at min modulation at around 7 to 10 degs, you basically want to output half your design heat load. So about 2kW in your case.
SimonD Posted 1 hour ago Posted 1 hour ago 41 minutes ago, MrWhat said: I have no zoning. My heat loss calcs are showing worst case 5kw which was LoopCAD and as low as 3.9kw (1 air change per hour) 4.7kw (2 ACPH) using Jeremeys spreadsheet from this forum. Obviously air changes per hour are a guess at this stage . He has based this on the build information i have given him at the moment. He has said that the heat pump looses 25% efficiency on defrost cycle which is the reason for recommending the larger pump. Its a 5 bed 350m2 ICF build Viessmanns always sound too big because of the way they label them. Go and double check the specs directly from either Viessmann or ViessmannDirect because IIRC the 8kW 150-A has a rated output of 4kW at A2/W35, 5.6kW at A7/W35 and 6.5kW at -7/W35. At 7C it'll modulate down to 2.1kW. The output range is 1.8-6.8kW. The 6kW unit does about 5.5kW? at -7/W35 I think. Somewhere there are nice charts published by Viessmann showing performance throughout the operating range at min and max outputs which honestly show the reduction in output between 5C & 0C. I don't think your designer is that far off, but slightly hedging bets on the defrost.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now