crispy_wafer Posted 6 hours ago Posted 6 hours ago Just running through my Grant ASHP schematic before I start putting pipes together. Schematic wants a close coupled tee, what does it do?
JohnMo Posted 5 hours ago Posted 5 hours ago CCTs provide hydraulic seperation - are you doing a mixed radiator plus UFH system?
crispy_wafer Posted 5 hours ago Author Posted 5 hours ago (edited) No, I've planned as just UFH, but... being the chap I am I've run 3 pairs of MLCP pipework for 1st floor rads/fancoils back to the plant room if the need ever arose! Edited 5 hours ago by crispy_wafer
crispy_wafer Posted 3 hours ago Author Posted 3 hours ago So, UFH fed from ASHP, my design flow rates are approx 17l/m. The internal pump on the Grant can do 20l/m. I don't mind straying from the schematic. So, if I remove the pump and mixing valve from the manifold, then pipe straight into the UFH. In the plant room I'll have the auto bypass and then the two port valve for the UFH zone. Can I locate a blending valve in the plant room, or does this need to be situated close to the manifold?
Nickfromwales Posted 3 hours ago Posted 3 hours ago 11 minutes ago, crispy_wafer said: Can I locate a blending valve in the plant room, or does this need to be situated close to the manifold? For what purpose?
crispy_wafer Posted 2 hours ago Author Posted 2 hours ago 1 minute ago, Nickfromwales said: For what purpose? My understanding (please correct me if I'm wrong) to protect the ufh circuit and floor coverings from over temperature should mogwai eat cookies after midnight and turn into a gremlin and takeover the system! Seriously though, I'm trying to learn, this bit of my Self build is a new topic for me! I would put it off for a little longer, but I need to get that last bit of wall boarded over so I can the plasterer in to finish the skimming.
Nickfromwales Posted 2 hours ago Posted 2 hours ago 4 minutes ago, crispy_wafer said: My understanding (please correct me if I'm wrong) to protect the ufh circuit and floor coverings from over temperature should mogwai eat cookies after midnight and turn into a gremlin and takeover the system! Seriously though, I'm trying to learn, this bit of my Self build is a new topic for me! I would put it off for a little longer, but I need to get that last bit of wall boarded over so I can the plasterer in to finish the skimming. You either need a pump to ‘suck’ through a traditional TMV, or to get an ESBE motorised mixer to run off the heat pump. You never see the TMV after a pump, as it needs the recirculating water to function / reference the temp of the water in the loops. If you're having a TMV for Justin, you'll need to leave the manifold as-is.
crispy_wafer Posted 2 hours ago Author Posted 2 hours ago 36 minutes ago, Nickfromwales said: You either need a pump to ‘suck’ through a traditional TMV, or to get an ESBE motorised mixer to run off the heat pump. You never see the TMV after a pump, as it needs the recirculating water to function / reference the temp of the water in the loops. If you're having a TMV for Justin, you'll need to leave the manifold as-is. Thankyou, that advice works for me
JohnMo Posted 1 hour ago Posted 1 hour ago If from heat pump, there is zero need for a mixing valve or additional pump. What Grant heat pump? The R290 has a modulation circulation pump so it will modulate flow rate to match demand - but doesn't do cooling ever, as no option available. R32 will do cooling but not if installed as per Grant instructions.