Annker Posted 18 hours ago Posted 18 hours ago (edited) I'm looking to buy cast iron radiators to install downstairs in a victorian renovation. Cast iron radiator centre are a supplier that seem to be competitively priced, if not one of the cheapest suppliers on the market. A potential catch which I am trying to resolve is the accuracy of their claimed performance (watts). I asked AI to compile a table and it illustrates as I thought, that CIRC claim their sections put out ~25% to 30% more heat than most other brands. As these sections are pretty much the same design, and I imagine are produced from same material, across all brands it seem like a claim worth verifying. Has anyone ever had the similar query? The heating system will be ASHP so I'm keen to match the respective heat loss figures for each room accurately and Obviously I don't want to end up with undersized rads. . 3-Column Cast Iron Radiator Output Comparison (~745-750mm Height) Per-Section Output @ ΔT50 Manufacturer Model Height Watts/Section Cast Iron Radiator Centre (CIRC) Traditional Victorian 3-Col 745mm 115W Shelbourne (CI Radiators 4u) 3-Column 745mm 86W Paladin Victoriana 3-Col 745mm 86W Arroll Neo-Classic 750 745mm 92W Carron Victorian 3-Col 745mm 80W Edited 18 hours ago by Annker
SteamyTea Posted 17 hours ago Posted 17 hours ago Cast Iron has a thermal conductivity (k) of around 52 W.m-1.K-1. Mild Steel is similar. So it just comes down to the thickness really. if they have the same mass for a similar surface area, they they will perform, near enough, the same. (it is a bit more complicated than that as fins, and fluid to surface area ratio can make a difference, but you get the idea) 1
Annker Posted 15 hours ago Author Posted 15 hours ago 1 hour ago, SteamyTea said: Cast Iron has a thermal conductivity (k) of around 52 W.m-1.K-1. Mild Steel is similar. So it just comes down to the thickness really. if they have the same mass for a similar surface area, they they will perform, near enough, the same. (it is a bit more complicated than that as fins, and fluid to surface area ratio can make a difference, but you get the idea) Well that's what I'm assuming also; that is given that the designs, or material used are not significantly different, the outputs should be more or less the same. So the question is whether 4/5 brands are understating the performance of their product or one brand is overstating their performance. The latter seems more likely. AI suggested that I request their BS EN 442 test documentation to verify the claim output. I will do that tomorrow and imagine more than likely be met with silence.
SimonD Posted 15 hours ago Posted 15 hours ago Here is the technical sheet for Stelrad cast iron. There 4 column are about 100W mark per section at 760 high. 28968_Stelrad-HS_Cast-Iron-Column_Web-PDF.pdf 1
Annker Posted 14 hours ago Author Posted 14 hours ago 20 minutes ago, SimonD said: Here is the technical sheet for Stelrad cast iron. There 4 column are about 100W mark per section at 760 high. 28968_Stelrad-HS_Cast-Iron-Column_Web-PDF.pdf 2.65 MB · 0 downloads Adds a bit more context that the Cast iron radiator centre are claiming that their 745mm high 3 column section has greater output than the Stelrad 760mm high 4 column section. It just doesn't seem likely to me. The thing is that CIRC seem to be a lot less expensive than all other suppliers, even if in reality you need to size up from their performance tables. I just want to make sure I get genuine performance figures from them.
Annker Posted 14 hours ago Author Posted 14 hours ago I've also noticed that CIRC state that a 4 column 760x1310 has an output of 2400W; where as their 3 column 745x1310 has an output of 2403W. A smaller section with one less column having a greater(albeit slightly) output surely cannot be correct or am I missing something?
Gus Potter Posted 13 hours ago Posted 13 hours ago 4 hours ago, Annker said: I'm looking to buy cast iron radiators to install downstairs in a victorian renovation. I had a loom at this for my own house as wanted soemthing similar. 4 hours ago, SteamyTea said: Cast Iron has a thermal conductivity (k) of around 52 W.m-1.K-1. Mild Steel is similar. So it just comes down to the thickness really. True but what I cloked was this. @Anneker, I'm going to be a gent and say you are not as old as I. When I came back from Kenya to complete my secondary educuation Scotland was cold.. but the school really did have some real cast iron radiators. From memory the fins were about 150 mm thick and oval. The flow went in the top and out the bottom. The modern equivalent (replica) has the flow in the bottom and out also at the base. To make it work (modern column radiator) you need to fit a baffle at the inlet at the base.. which basically makes it almost work like a modern radiator. Now the baffles are not perfect hence the likely discrepancy you see. Architectural radiators need to make a compromise between performance and design look.. there is no free lunch. I would if I was you chose the thing you like, over size it a bit, say by 20%, fit a thermostatic valve. Make sure you have a good diameter flow and return pipe to it. In the round all this may cost you £100 quid more but I bet the paint on the walls is going to cost you more than that? Keep posting! Gus
Annker Posted 2 hours ago Author Posted 2 hours ago 10 hours ago, Gus Potter said: Now the baffles are not perfect hence the likely discrepancy you see. Architectural radiators need to make a compromise between performance and design look.. there is no free lunch. Hi Gus, To my mind this is not the issue, as I am comparing one cast iron radiator section against another. I called CIRC and as expected they can't give a specific reason why their section is upwards of 25% more efficient than all others, but they can say that no customer has raised this issue before. Is it just my experience or do the majority of building product suppliers in the UK seem clueless about their products. Anyway, as you also suggest I think if I use CIRC it is wise to oversize. My AI assistant summarises as such: Bottom line: With an ASHP, the risk profile is asymmetric. Undersized radiators force higher flow temperatures and reduce efficiency. Oversized radiators allow lower flow temperatures and improve efficiency. If you must err, err on the side of larger. Sizing to Paladin/Carron figures while buying from CIRC is a sensible, low-risk strategy. Worst case: you've got slightly more efficient heating and spent a bit more on radiators. Best case: you've sized correctly.