Replacement pump recommendation

Featured Replies

  • Author

To revive a recently deceased thread!


turns out that the system was still causing problems and so  I have had it changed over to a pressurised system.

one question on the install - I had assumed that there would be a tundish by the expansion vessel but there doesn’t appear to be. Is what you can see in the picture a suitable alternative?

 

IMG_4234.jpeg

IMG_4235.jpeg

  • Replies 53
  • Views 4.3k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • John Carroll
    John Carroll

    Open & shut the pump isolating valves 3 or 4 times, should then hold OK.   I have a 6M Wilo Yonos Pico Pump, running fine and silent for the past 7 years.

  • Nickfromwales
    Nickfromwales

    Not the stems, just the pump nuts. Also, brass doesn’t rust so it’s the pump that’s corroding not the valves.    Very likely the original pump has those nasty rigid washers, not the modern, mor

  • Nickfromwales
    Nickfromwales

    Try again, lol.

Posted Images

18 minutes ago, jfb said:

I had assumed that there would be a tundish by the expansion vessel but there doesn’t appear to be. Is what you can see in the picture a suitable alternative?

 

Where does the discharge pipe go? There should be some easy means to see if the prv is letting by so either a tundish or a pipe termination outside where the pipe is turned back on itself towards the wall to stop hot, over-pressure release squirting into someone.

  • Author
9 hours ago, SimonD said:

pipe termination outside where the pipe is turned back on itself towards the wall to stop hot, over-pressure release squirting into someone.

It has this yes

 

11 hours ago, jfb said:

To revive a recently deceased thread!


turns out that the system was still causing problems and so  I have had it changed over to a pressurised system.

one question on the install - I had assumed that there would be a tundish by the expansion vessel but there doesn’t appear to be. Is what you can see in the picture a suitable alternative?

 

IMG_4234.jpeg

IMG_4235.jpeg

It doesn’t need a tundish as it’s not potable water.

 

The reason you have a tundish on potable is that it’s a constant pressure, so if you’re letting cold mains water go to outside / drain then it needs to be visible so you do something about it. WRAS requires this. 
 

With your heating system it’s only got the pressure held within to release, then there’s nothing else to come out until you open the filling loop back up to refill it.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.