Potatoman Posted yesterday at 07:38 Share Posted yesterday at 07:38 Hi, is there a calculation you can make to determine the daily COP of a system. Thanks Link to comment Share on other sites More sharing options...
JohnMo Posted yesterday at 08:08 Share Posted yesterday at 08:08 Measured heat output or calculated for flow/return temp and actual flow rate. All electrical energy use - timer, controllers, all pump, immersions etc. Divide heat out by electric in. Link to comment Share on other sites More sharing options...
SteamyTea Posted yesterday at 08:11 Share Posted yesterday at 08:11 Usually the system has a built in display that can show it. They are sometimes a bit misleading though. You can calculate it yourself, but you really need some monitoring equipment. This would usually be data loggers on the flow and return pipes to log the temperature, a flow sensor to measure the mass of fluid pumped around and an electrical logger to measure the energy input. Then the arithmetic starts. Calculate the output. Specific heat capacity [SHC] of fluid, 4 is close enough for this [kJ.kg-1.K-1] Flow rate [kg.h-1] Temperature Delta between flow and return in kelvin [ΔT] This will give you the kilojoules over the time period measured [kJ]. You can convert kilojoules to kilowatt.hour by multiplying by 0.0002778. It is usual to place a subscript to distinguish the type of energy delivered, in this case a t for thermal is used. kJ.kg-1.K-1 x kg.h-1 x ΔT x 0.0002778 = kWht Electrical logging is usually calculated in mean power [W] or total energy [Wh]. Care must be taken here as they are not the same thing. Energy is power multiplied by time. Energy is usually purchased by the kilowatt.hour so divide by 1000. Again a subscript e is used to show that it is electrical energy. (W x h) / 1000 = kWhe The coefficient of performance [CoP] is the ratio of the output to the input energies. CoP = kWht / kWhe 1 Link to comment Share on other sites More sharing options...
Bramco Posted yesterday at 09:03 Share Posted yesterday at 09:03 47 minutes ago, SteamyTea said: you really need some monitoring equipment The open energy monitor guys do a kit -> https://shop.openenergymonitor.com/level-3-heat-pump-monitoring-bundle-emonhp/ And they have a site showing the data from people who have installed the kit and made their data public -> https://heatpumpmonitor.org/ 1 Link to comment Share on other sites More sharing options...
FarmerN Posted yesterday at 11:47 Share Posted yesterday at 11:47 3 hours ago, SteamyTea said: Usually the system has a built in display that can show it. They are sometimes a bit misleading though. Feel my display must be misleading , showing a COP of 6 for December so far, Too good to be true ?? My GSHP is a NIBE S1155 12 KW , with 600M ground loop, heating a 215sqM new build+ DHW December 179 kWh in 1073 kWh out. Brine in at 8.8 Deg C , main living space 21Deg C , bedrooms 19 Deg C DHW 48 Deg C Link to comment Share on other sites More sharing options...
PhilT Posted yesterday at 12:09 Share Posted yesterday at 12:09 3 minutes ago, FarmerN said: Feel my display must be misleading , showing a COP of 6 for December so far, Too good to be true ?? My GSHP is a NIBE S1155 12 KW , with 600M ground loop, heating a 215sqM new build+ DHW December 179 kWh in 1073 kWh out. Brine in at 8.8 Deg C , main living space 21Deg C , bedrooms 19 Deg C DHW 48 Deg C If you can get the data, John Cantor has a nice easy calc template, so you can at least sense check the output power. https://heatpumps.co.uk/heat-pump-resources/numbers-and-calculations/ Link to comment Share on other sites More sharing options...
Beau Posted yesterday at 12:18 Share Posted yesterday at 12:18 28 minutes ago, FarmerN said: Feel my display must be misleading , showing a COP of 6 for December so far, Too good to be true ?? My GSHP is a NIBE S1155 12 KW , with 600M ground loop, heating a 215sqM new build+ DHW December 179 kWh in 1073 kWh out. Brine in at 8.8 Deg C , main living space 21Deg C , bedrooms 19 Deg C DHW 48 Deg C Thats a very good brine temp. If your heating flow temps are low I would have thought a COP of 6 is within reach. 1 Link to comment Share on other sites More sharing options...
Potatoman Posted 23 hours ago Author Share Posted 23 hours ago Can anybody tell me if this calculation holds water. Heat loss calculation of my house is 5.8Kw at -2 for 21 degrees inside. So to raise the temperature of my house I require 252w/degree 5800 divided by temp difference 23 So if you take average outside temp - average inside temp 0-21 =21 21 x 252 = 5292w 5.3kW x 24 = 127 kWhr/day divided by the actual kWHr used, in this case 41 kWHr would this give a COP of 3.097 ? Link to comment Share on other sites More sharing options...
JohnMo Posted 21 hours ago Share Posted 21 hours ago In theory it may be ok, but heat loss is best guess, and the -2 is unlikely to stay constant all day, so could be correct, but may not be. At that temp outside you could have a bunch of defrosting happening also to confuse things. Link to comment Share on other sites More sharing options...