Dave Jones Posted Wednesday at 07:11 Posted Wednesday at 07:11 get the roll of electric cable before you dig and lay it as you go. if you have bends it will 100% snag in that horrible felxi duct. Otherwise use sewer pipe instead of the flexi and it will be a breeze to pull through.
Temp Posted Wednesday at 09:17 Posted Wednesday at 09:17 2 hours ago, Dave Jones said: Otherwise use sewer pipe instead of the flexi and it will be a breeze to pull through. I was told our electric co was fussy about ducts and it had to be a smooth bore solid wall pipe printed with some standard on the outside (at least for the bit from road to house).
Mr Punter Posted Wednesday at 15:55 Posted Wednesday at 15:55 6 hours ago, Temp said: I was told our electric co was fussy about ducts and it had to be a smooth bore solid wall pipe printed with some standard on the outside (at least for the bit from road to house). +1 and the DNO do not allow you to run electric through sewer pipe or non approved ducting. 1
kandgmitchell Posted Wednesday at 16:47 Posted Wednesday at 16:47 7 hours ago, Temp said: I was told our electric co was fussy about ducts and it had to be a smooth bore solid wall pipe printed with some standard on the outside (at least for the bit from road to house). Mine certainly was - I had to search hard to find the larger duct for their three phase cable as only a few places kept it in stock