Harry13 Posted August 10, 2024 Posted August 10, 2024 Hi all, I’m currently building a garden room and have a question regarding the flat roof I plan on installing. The room is 5.3x5.3 outside walls and internal walls are 4.7x4.7 I’d like to know if 8x2 joists @400 centres will suffice over this distance, installing an rsj is not an option for me due to doors and window lintel sizes and positioning. Many thanks
DevilDamo Posted August 10, 2024 Posted August 10, 2024 No, you would need to install 47 x 220mm C24’s at 400mm c/c. What are the walls constructed of? What is the overall height snd how close to a boundary are you?
Harry13 Posted August 10, 2024 Author Posted August 10, 2024 Hi and thanks for the reply. The overall height will be 2.5m once the 220 joists and roof deck and coverings are installed. 1 metre away from the boundary. So just to confirm I’d be looking at 2x9 for the joists? I’ve had someone else tell me that I should be using 3x9, not sure if that overkill, that said I’d rather have it as strong as possible. many thanks
garrymartin Posted August 10, 2024 Posted August 10, 2024 Using C16 timber, 47 x 220mm (roughly 2x9) will suffice for the clear span you will have and will allow you to be more efficient with your insulation. "3x9" is indeed overkill. If internal height is an issue, then moving to 63 x 195mm C16 will give you an extra "inch" but will reduce insulation performance. You could also use C24 timber, allowing 47 x 195mm or 63 x 170mm. See https://www.timberbeamcalculator.co.uk/en-gb/span-table/flat-roof-joists?load=0.75&class=C16 for C16 and https://www.timberbeamcalculator.co.uk/en-gb/span-table/flat-roof-joists?load=0.75&class=C24 for C24 timber.
DevilDamo Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 12:51, garrymartin said: Using C16 timber, 47 x 220mm Expand Quite concerning how different the tables you’ve referred to differ to the standard Trada tables as the latter don’t confirm your size.
DevilDamo Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 12:22, Harry13 said: to confirm I’d be looking at 2x9 for the joists? Expand Yes, but play it safe using C24’s and not C16’s. Is it being constructed with masonry walls?
garrymartin Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 15:31, DevilDamo said: Quite concerning how different the tables you’ve referred to differ to the standard Trada tables as the latter don’t confirm your size. Expand Do you have a link to the Trada tables you're looking at? Perhaps the parameters are different? I've assumed access for maintenance and repair only. Are you also looking at the "clear span" of approximately 4.7m? These two links are Eurocode 5 compliant spans (as per Trada); https://www.taylormaxwell.co.uk/uploads/files/D.100.01-01_C16-Span-Tables_Design_Span-Tables.pdf https://www.taylormaxwell.co.uk/uploads/files/D.100.02-01_C24-Span-Tables_Design_Span-Tables.pdf
Harry13 Posted August 10, 2024 Author Posted August 10, 2024 Hi, the walls have been made with concrete blocks and there are 2 leafs with a cavity. External wall measures 5.3m on the outside edge and the internal leaf is 4.7m on the inside. Thanks
DevilDamo Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 15:54, garrymartin said: Do you have a link to the Trada tables Expand Not a link but I have them saved. None of the C16 tables justify a 4.7m clear span with 47x220mm @ 400c/c
garrymartin Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 19:53, DevilDamo said: Not a link but I have them saved. None of the C16 tables justify a 4.7m clear span with 47x220mm @ 400c/c Expand I'm lost??? Is there perhaps something I'm misunderstanding in the tables? The first table clearly shows a 5.00m clear span for a 47x220mm C16 @ 400 centres (Table 7.1) and the second table shows a 4.89m clear span for a 47x220mm C16 @ 400 centres (Table 7.3)
DevilDamo Posted August 10, 2024 Posted August 10, 2024 Incorrect dead load. You need to take the middle section of each table.
garrymartin Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 20:33, DevilDamo said: Incorrect dead load. You need to take the middle section of each table. Expand I suppose we should have asked what the roof make-up would be. Pretty sure when I did the calculations for my roof, the dead load was less than 0.5 kn/m2 for 18mm plywood, EDPM, internal 12.5mm plasterboard, skim, and insulation. Do you have something that would give me some advice on when to use 0.5, 0.75, and 1.0 ratings? Is there any specific roof make-ups to dead load comparisons?
garrymartin Posted August 10, 2024 Posted August 10, 2024 (edited) I'm clearly doing something wrong or fundamentally misunderstanding the calculations. I've just repeated my roof calculations as follows; 12.5mm plaster + skim = 0.2 kn/m2 XPS insulation = 0.04 kn/m2 18mm plywood = 0.1 kn/m2 1.52mm EPDM = 0.02 kn/m2 The total for that is 0.36 kn/m2 so well below 0.5 kg/m2. @DevilDamo Am I doing something wrong or misunderstanding some part of the calculations? Or is it just we didn't clarify what the proposed roof make-up was? Edited August 10, 2024 by garrymartin noted as 0.36 kg/m2 and should have been 0.36 kn/m2
DevilDamo Posted August 10, 2024 Posted August 10, 2024 I was initially comparing your figures to mine… both using a dead load of 0.75 and that is what/why I said they were different.
garrymartin Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 21:28, DevilDamo said: I was initially comparing your figures to mine… both using a dead load of 0.75 and that is what/why I said they were different. Expand I think we've inadvertently confused the hell out of @Harry13 Harry, just make sure to use C24 timber! 🤣
ETC Posted August 10, 2024 Posted August 10, 2024 https://www.buildingcontrol-ni.com/assets/pdf/TechnicalBookletD2012.pdf
garrymartin Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 21:48, ETC said: https://www.buildingcontrol-ni.com/assets/pdf/TechnicalBookletD2012.pdf Expand Not sure that helps loads - it's an old document and for Northern Ireland...
ETC Posted August 10, 2024 Posted August 10, 2024 (edited) On 10/08/2024 at 21:54, garrymartin said: Not sure that helps loads - it's an old document and for Northern Ireland... Expand It’s a current document and physics is still physics irrespective of where you are in the UK. Edited August 10, 2024 by ETC
garrymartin Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 21:56, ETC said: It’s a current document and physics is still physics irrespective of where you are in the UK. Expand 🤣 Fair comment. Though the tables don't have the same numbers in them... 😉
ETC Posted August 10, 2024 Posted August 10, 2024 On 10/08/2024 at 22:00, garrymartin said: 🤣 Fair comment. Though the tables don't have the same numbers in them... 😉 Expand Of course they don’t - they’re for different imposed loads which vary for location.
SteamyTea Posted August 11, 2024 Posted August 11, 2024 (edited) On 10/08/2024 at 21:56, ETC said: physics is still physics irrespective of where you are in the UK Expand The force of gravity, and therefore time, changes depending on altitude and ground density. All the granite in Cornwall makes it 20 years behind the times. Edited August 11, 2024 by SteamyTea 2