I have enough space on our plot for a south facing ground array along the northern fence line of our garden.

Probably cannot afford to actually install this day one but if there is any money left ( yeah i know)once we move in i would like to put an array in place.

So the question is what cables and at what depth should i lay down, just in case. The consumer unit at the front of the house on the west side is 21 metres from the closest point that the array would be sited.

Thanks as always

keith

 

Posted
  On 17/04/2024 at 21:00, Post and beam said:

I have enough space on our plot for a south facing ground array along the northern fence line of our garden.

Probably cannot afford to actually install this day one but if there is any money left ( yeah i know)once we move in i would like to put an array in place.

So the question is what cables and at what depth should i lay down, just in case. The consumer unit at the front of the house on the west side is 21 metres from the closest point that the array would be sited.

Thanks as always

keith

 

Expand  

Bit of a vague question without specifics about volts and amps. Or just duct with a pull rope then specifics can be sorted later.

 

You may be best to size the cable for DC instead of AC as DC tolerate voltage drop more easily.

 

Amoured cable can be surface run, so could follow a fence line for example.

Posted

Ours is similar. We laid a 4 core armoured cable for DC in a trench, as @SteamyTea says at least half a metre deep. Use 4 core, so you can have your array in 2 halves, into separate MPPT connections on the inverter.

 

If you aren't going to install it immediately, get the sparky to install a spur to where you expect the inverter to installed and get that on the electrical certificate labelled 'solar PV'. This allowed us to do a self install and produce the electrical cert to national grid which they were happy enough with to give us the all clear on the installation.

 

Once National Grid were happy, Octopus were also happy to put us on one of their smart tariffs.

 

That way you avoid the dreaded MCS tax...

 

Simon

Posted
  On 17/04/2024 at 21:16, Mattg4321 said:

Much better installing a duct with a rope through. 

Expand  

Thanks and yes i thought that was the way to go. As stated above, is 500mm deep appropriate?

  On 18/04/2024 at 07:26, Bramco said:

get the sparky to install a spur to where you expect the inverter to installed and get that on the electrical certificate labelled 'solar PV'.

Expand  

Thanks for this as well, good idea.

 

As to JohnMo's point about being vague, yes totally accept that. That'll be my ignorance of this subject.  As it stands today i have no idea if the local rule makers will allow me to put an array in or of what size. It a conservation area.  I understand local micro inverters are the current idea.

 

The available fence line space would allow me a 30 metre run of panels on their ' long side' horizontal, if i do a single run. Neighbours on the other side of the fence would then not even see the array so no nuisance value to them.

Posted
  On 18/04/2024 at 08:08, Post and beam said:

I understand local micro inverters are the current idea

Expand  

They for for extracting the best performance out of a shading compromised array.

Actually, they were for installers to make a few extra quid in most installations.

Posted
  On 17/04/2024 at 21:25, JohnMo said:

Bit of a vague question without specifics about volts and amps.

Expand  

As i dont have the knowledge to answer this yet. Is there a table or a calculation i can use that would for example provide the necessary info for a 4, 6, 8 & 10kw array. or whatever is practical/allowed/sensible.

The house will be 200 square metres, UFH, Vaillant 7kw ashp, compulsory EV point out front.

Posted
  On 18/04/2024 at 14:19, Post and beam said:

As i dont have the knowledge to answer this yet. Is there a table or a calculation i can use that would for example provide the necessary info for a 4, 6, 8 & 10kw array. or whatever is practical/allowed/sensible.

The house will be 200 square metres, UFH, Vaillant 7kw ashp, compulsory EV point out front.

Expand  

Can't your spark size the cable for you? He's gonna be signing off the install so getting him to spec the cable should minimise any problems.

Posted
  On 18/04/2024 at 19:06, Dillsue said:

Can't your spark size the cable for you? He's gonna be signing off the install so getting him to spec the cable should minimise any problems.

Expand  

If and when we get to that stage yes of course. But i like to learn. 