Good evening.

I had the boiler installed last year and have been losing pressure on the heating side without any trace of leaks. Also had two overnight drops in  ch water pressure causing the boiler to fail to operate about 4 months ago. I have removed the condensate line tonight to see if it could be a passing valve. Ive noticed i have a 15mm bend to the boiler from 22mm gas supply which i believe may be undersized. The flue also drips as it is not angled correctly . Does anyone have similar issues with this boiler or suggestions.

Thanks

Link to comment
Share on other sites

Ok. Still loosing pressure and water present in the expansion tank when shreger valve tested. Dont have any high pressure issues apparent as is normal.  I think something may have happened in the  summer as shower wouldn't get warm one morning an found the system pressure was zero from about 1.3 bar a few days before.

Link to comment
Share on other sites

41 minutes ago, dave1967 said:

Ok. Still loosing pressure and water present in the expansion tank when shreger valve tested. Dont have any high pressure issues apparent as is normal.  I think something may have happened in the  summer as shower wouldn't get warm one morning an found the system pressure was zero from about 1.3 bar a few days before.

 

So, you've found the issue. From what you've written it sounds like you're still looking though? 

Link to comment
Share on other sites

Ok. Still loosing pressure and water present in the expansion tank when shreger valve tested. Dont have any high pressure issues apparent as is normal.  I think something may have happened in the  summer as shower wouldn't get warm one morning an found the system pressure was zero from about 1.3 bar a few days before.

Link to comment
Share on other sites

14 hours ago, dave1967 said:

Still loosing pressure and water present in the expansion tank when shreger valve tested

You expansion tank, has a diaphragm in it, water side and air side. The Schrader valve is on the air side - t should be dry.  As stated on Monday it is likely to be an issue with the expansion tank. Order new part, replace, done - or call your plumber to have him do it. But strictly speaking, as the expansion vessel is within the boiler casing, you should be having a gas safe plumber doing the job.

Link to comment
Share on other sites

Ok they came out. 

Said water in expansion tank is not always an issue with viessmamm 100. 

It was pressured up again with a pump.

Prv was ok. Not sure what else he did but said it was not set up correctly for external control which he fixed. Not Sure how that was the main issue as it been fine for 10 months but seems ok now and no pressure loss.

So all good.

 