Could someone help?
If I know there is air flowing through a 100mm duct at .80m per second, how do I compute that to m3 per hour?
Edited by Coanda
π x r2 = area of pipe
3.1416 [π] x 0.052 [m] = 0.007854 [m²]
Flow rate x area = volume per unit time.
0.8 [m/s] X 0.007854 [m²] = 0.0062832 [m³/s]
3600 seconds in an hour.
0.0062832 [m³/s] x 3600 = 22.61952 m³/h
For bonus marks
Approximate density of air 1.25 kg/m³
22.61952 [m³/h] x 1.25 [kg/m³] = 28.2744 kg/h.
Specific heat capacity of dry air approximately 1 kJ/kg.K
So to heat (or cool) 28.3 kg by 1K will take.
28.3 [kg] x 1 [kJ/kg.K] x 1 [K] = 28.3 kJ
To convert to kWh, multiply by 0.00027778 (1 / 3600 [s])
28.3 [kg] x 0.00027778 = 0.007861111111 kWh.
As this relates to the flow rate per hour, dividing by 1 hour will give the power, in kW, multiply by 1000 will convert it to watts.
0.007861111111 [kWh] x 1000 = 7.9 W.
I think, please check.
Edited by SteamyTea
7 minutes ago, saveasteading said:
Oops that was for 1m/s
So 28.26 x 0.8
= 22.6.
Easy error to make, I usual reduce to a reciprocal and then multiply at the end.
Then forget.
4 hours ago, Coanda said:
Could someone help?
BTW it is normal to have the answer in litres/second for MVHR calculations.
I have never understood why, we have SI units to make life simple.
Because it's easier for most people to imagine 9 litres per second rather than 32.4 cubic metres per hour, that said SI units do make life simpler. I do hate it when people use centimetres rather than millimetres.
1 minute ago, Coanda said:
Thank you one and all.
I was very good at math in school but alas, that was a long time ago.
You have to use it to very day. Even then it is easy to make errors.
The house is measured in metres so its volume in m3 is an easy calculation, air changes an hours (ACH) is m3/h - an easy outcome, so the maths in the same units is super simple. Changing the litres/second don't see the point.
House 200m2, 2.5m tall, is 500m3, 0.5ACH, is 250m3/hr.  All maths done in the head, my flow meter works in the same units, you just need to work out the room flow rates from there. Why bother the litres/sec
In the US of A, they measure houses in feet, but oddly don't use fluid oz for volume, they stick to cubic feet per minute.
As an aside, when I listen to energy traders/experts on the radio talking about 'the energy crisis', they keep talking about the price of a therm pf gas.
And the government uses barrel of oil equivalent in reports.
And how often do we hear someone say they use a lot of energy, then say it is "£300 a month".
SI and the derived units are so easy to understand.
A utube video I saw from the USA talked about ton units for MVHR or was it aircon.
Is Aircon.
Think it is the amount of energy to cool a ton of water 1⁰f.