Is it a single 3 way valve or multiple 2 way valves.  Either way it sounds like the valve to the hot water tank not opening so there is not enough flow.  that could be a faulty actuator head or it could be a mechanical fault (seized) If you don't know, post a picture of the HW tank and all valves or controls on or near it.

Link to comment
Share on other sites

As above. I had this problem last year although it was the other way round. We had multiple two way valves and one of the actuator heads had failed which is a common fault.  Easy to replace. 

Edited by Kelvin