Cool Energy - Alarm code AL114

Featured Replies

So, as soon as I comment that things are working well with our Cool Energy iVT-18 ASHP, I notice the control panel is showing an alarm code AL114. Not a very helpful message to describe it: "Power+ alarm:Power+ offline".

 

I've tried the "IT solution" turn off leave a few mins and turn on - still the same.

 

If anyone has seen this before or has suggestions please let me know as would be nice to try a few things before contacting them at Cool Energy as they seem not to be there at the mo.

 

1 hour ago, Adam2 said:

So, as soon as I comment that things are working well with our Cool Energy iVT-18 ASHP, I notice the control panel is showing an alarm code AL114

 

Your fault... You prodded the 'reality generator'.

 

Sometimes chinese firmware copies over numbers like these. Variously AL114 has meant:

  • Power+ alarm:Power+ offline (Carel)
  • memory backup battery fault (Carel)
  • Probe B2 alarm (Carel)
  • room thermostat fault (Aermec)
  • Power+ alarm: Drive connection alarm (EMAUX)

Not much help I guess.

  • Author

So, I used the app to change to heating only (as it was stuck on hot water cylinder priority I guess) then turned off for 15 mins. Turned on and all OK on heating and no more alarm ! 🙂 Left that for a while to get the buffer up to temp then put back to heating + hot water and after a short time it switched to hot water and seems OK. So emergency over 🙂 Will try and find the cause but if happens again I guess try the same but this is the first occurrence since installed in March - though does probably coincide with the first cooler night (8 degrees). If I find a possible cause will share on here for others 

The inverter looks like it tripped off the bus. I've had mine do this if power cycled too rapidly, have you seen any mains dips?

Because the installation instructions discusses  problems when the voltage drops, we had installed the next size cable up for the distance and ampage to reduce the risk of voltage drop and installed a type C RCBO 

Power+ alarm:Power+ offline

 

The Power+ is the inverter/vfd that drives the compressor. It’s connected to the main Carel pCO control PCB via rs485/modbus.

 

This error would imply that the Power+ hasn’t powered on properly, so isn’t responding to commands from the pCO.

 

  • Author

Very interesting, will see how this goes and if happens again look at cable size

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.