Radian Posted September 7, 2022 Share Posted September 7, 2022 I've been trying to reduce the flow temperature of our 30kW condensing system boiler to improve it's efficiency. The lowest I can practically operate it and have HW at 55oC, is with a flow temperature of 65oC. Any smaller difference results in extended running and short cycling. As this chart shows for the start of today, the cylinder temperature sensor governing the HW demand fell just below the overnight minimum setback temperature of 40oC and very briefly fired up the boiler at 4:56AM. The hysteresis is programmed at 2.5oC so the boiler demand ceased 8 minutes later at 5:04AM as the cylinder sensor reached 42.5oC Notice, however, that the temperature in the HW cylinder continues to rise to almost 50oC over the next 10 minutes which is how long the boiler overrun is programmed to be. This is another area that could do with more examination as it seems there was still plenty of energy to be transferred from the heat exchanger and pipe work. But the real issue comes at 7AM when the daytime temperature demand of 55oC kicks in. Initially the temperature rises quite quickly as it did earlier, due to the full 30kW being applied. But on reaching 51oC the boiler starts modulating and the rate of heating falls (as witnessed by the change in slope). When the cylinder sensor reaches 53.3oC at 7:33 the boiler switches off completely and commences to cycle on and off at 10 minute intervals at its minimum output of 10kW. This strikes me as being inefficient as it's only at 8:13, 45 minutes later, when 55oC is finally attained and the boiler demand is removed. From this it seems to me as if a HW temperature setting of 53.3oC would be about the limit of what the system was comfortable with - as this is where we get to when modulating reaches its limit and the boiler starts cycling off and on. If I drop the flow temperature below 65oC then this will push down the HW temperature by a similar delta. By inference from the numbers above, a flow temperature of 60oC would mean something in the region of a maximum HW setpoint of 48oC for sensible operation. I think this would be too low, yet people talk of boiler flows of 55oC! At the setpoint of 65oC the boiler flow itself reaches a self-reported peak of 68oC just as it clicks off. The actual return temperature at this point is 56oC also according to the boiler diagnostics menu. My cylinder sensor is typically three or four degrees lower than the return temperature which seems reasonable. Am I wrong to see on/off cycling as undesirable once the turn-down is insufficient to keep the boiler delta happy? Link to comment Share on other sites More sharing options...
SteamyTea Posted September 7, 2022 Share Posted September 7, 2022 56 minutes ago, Radian said: Notice, however, that the temperature in the HW cylinder continues to rise to almost 50oC over the next 10 minutes which is how long the boiler overrun is programmed to be. When a cylinder is heated from the base, there is a fair amount of turbulence in it. Take away the heat source (no input to coil at base) and there will still be some turbulence for a few minutes. That needs to settle before a true 'spot' temperature reading can be taken. What does this mean? Link to comment Share on other sites More sharing options...
JohnMo Posted September 7, 2022 Share Posted September 7, 2022 Couple of things going on. A cylinder with a coil is designed to have around 75 degree flow temp going into it. As you reduce the flow temp the heat exchanger coil cannot transfer the heat away very well. When you get a certain point in the heating cycle the boiler will trip on a high return temp. Then go in to short cycling. As you are seeing. Not efficient. You may use less gas by ramping up the flow temp to 75, your return should be around 55. The heat cycle should be quite quick. Link to comment Share on other sites More sharing options...
SimonD Posted September 7, 2022 Share Posted September 7, 2022 What boiler make and model have you got? It's worth checking if it can be configured for priority domestic hot water. Some system boilers can't and are dependent on the same setting for both CH and DHW. And some boilers that can be configured that way don't tell you they can be so you have to figure it out. I can tell you that Ideal boilers can and it's very simple, giving 80 deg DHW and modulating CH even though the installation manual doesn't tell you this explicitly. Link to comment Share on other sites More sharing options...
Radian Posted September 7, 2022 Author Share Posted September 7, 2022 2 hours ago, SteamyTea said: What does this mean? It's an estimate of the gas consumption. 1 hour ago, JohnMo said: You may use less gas by ramping up the flow temp to 75, your return should be around 55. The heat cycle should be quite quick. If the return was 55 then yes it should be in condensing mode but in practice (my experience) a 75 flow will result in a return over 60 and lose out on efficiency. Obviously there's a trade-off here somewhere but it'd take some finding. 1 hour ago, SimonD said: What boiler make and model have you got? It's a Glowworm Flexicom 30hx The manual is very opaque on HW priority hinting that it all happens using auxiliary eBus control but I don't have that. Not unless I hack something together. Link to comment Share on other sites More sharing options...
marshian Posted October 2, 2023 Share Posted October 2, 2023 On 07/09/2022 at 15:02, Radian said: It's a Glowworm Flexicom 30hx The manual is very opaque on HW priority hinting that it all happens using auxiliary eBus control but I don't have that. Not unless I hack something together. Hi been reading this thread and your "zombie boiler" thread and found them very interesting Trying to keep this post short so I don't ramble on too much but in a nutshell I also have Glow worm Flexicom 24HX and am in a similar boat so to speak When installed it was running for several years at 75 deg flow temps due to T11 rads (legacy from the original house build) and a gas engineer who left the boiler providing enough heat but not optimised (probably never running in condensing mode) the temp was fine for CH or HW Last winter 4 T11's got swapped out for T22's and I was able to reduce CH flow temps to around 64 deg c and returns of around 45 but I had to heat water separately from CH by manually increasing flow temps to 68 which is a bit of a pain to have to do twice daily (return temps don't exceed 54 deg C) tank temp gets to high 40's which is fine for us as we pretty much use all the HW daily and it minimises losses (Tank gets a Legionaires once a week where the flow temp is set to 82 and the tank gets to just over 60 deg C) This summer a bunch of the remaining rads got swapped out for T22's or larger vertical rads in rooms with space issues (bathrooms and Kitchen) Now in the early autumn when CH is starting to be needed I can heat the house with 45 deg flow temps and 30 deg return temps - it may need to rise to 55 deg in the colder months but the return temps will still be lower and keep the boiler in condensing mode all the time. Controls is WISER with Smart TRV's on all but one rad although it now has an automatic by pass in circuit However HW is going to require the same manual work around again this winter so been searching the web for a solution and although I can't find the post I found a thread where an external weather comp sensor was used and small program / switch ran to change the resistance of the outside temp sensor to fool the boiler into ramping up the flow temp when HW was being called for I've found the savings in gas consumption between flow temps at 68 and several cycles compared to a higher flow temp say 75 and one or two cycles to achieve the same temp is minimal especially when the boiler is range rated down Wondered what your thoughts on the Weather compensation hack would be?? Link to comment Share on other sites More sharing options...
marshian Posted October 2, 2023 Share Posted October 2, 2023 One more thing - the parameters for anti cycle d.2 don't have much impact at higher boiler temps but the pump over run timer d.1 is set to 4 mins as std (mine was actually set to 2 mins for some reason and used to cycle a lot) - I've now increased d.2 to 8 mins and it gives much longer time for the HW tank to extract out all the heat (once the flow and return temps equalise the boiler with fire again if there is still a call for heat regardless of the pump over run setting) it's around 6 - 7 mins before it fires again Link to comment Share on other sites More sharing options...
Radian Posted October 5, 2023 Author Share Posted October 5, 2023 On 02/10/2023 at 23:14, marshian said: I found a thread where an external weather comp sensor was used and small program / switch ran to change the resistance of the outside temp sensor to fool the boiler into ramping up the flow temp when HW was being called for Sounds unlikely for a Flexicom? I don't think WC is available on the mainboard. d.2 is certainly worth increasing. Espc. if you've got an energy efficient pump. Link to comment Share on other sites More sharing options...
Andehh Posted October 5, 2023 Share Posted October 5, 2023 With the greatest of respects, this micro management is probably saving you the cost of a pint a month. Set the dials to 'e' and worry not! Focus on draft proofing and reducing usage! Link to comment Share on other sites More sharing options...
marshian Posted October 5, 2023 Share Posted October 5, 2023 2 hours ago, Radian said: Sounds unlikely for a Flexicom? I don't think WC is available on the mainboard. d.2 is certainly worth increasing. Espc. if you've got an energy efficient pump. Apparently if you have X41 on the PCB you can plug in an external temp sensor for weather comp functionality The instruction leaflet below shows what I mean https://www.glow-worm.co.uk/glow-worm/products-1/outdoor-sensor/0020266792-installation-instructions-1476886.pdf I saw you had another PCB that you were experimenting with and I was interested in if that had X41 on the board Link to comment Share on other sites More sharing options...
marshian Posted October 7, 2023 Share Posted October 7, 2023 On 05/10/2023 at 18:18, Andehh said: With the greatest of respects, this micro management is probably saving you the cost of a pint a month. Set the dials to 'e' and worry not! Focus on draft proofing and reducing usage! Flexicom HX don't have a dial or an "e" position You have "mode" "Digital flow temp display" and "-" and "+" In my case I've already reduced drafts to the point where I had to fit a PIV to manage the humidity gain and In 14 mths I've reduced gas usage from 15 - 16,000 kWh to 8,500 kWh per year. Link to comment Share on other sites More sharing options...