dave1967 Posted August 28, 2022 Share Posted August 28, 2022 Hi Looking for 8port manifold with actuators and wireless stats for each actuator. Using 15mm pipes and 22 from the boiler. Any guidance appreciated as struggling to find what im looking for. Link to comment Share on other sites More sharing options...
ProDave Posted August 28, 2022 Share Posted August 28, 2022 Why wireless stats and why one per manifold loop? Most UFH pipe is 16mm, could this be why you are struggling to find what you want? Link to comment Share on other sites More sharing options...
JohnMo Posted August 28, 2022 Share Posted August 28, 2022 here you go, they do 15mm euro cones for your pipes. I had good service from them. https://www.outsourcedenergy.co.uk/product-category/manifolds/underfloor-manifolds/ Suspect you will have lots of boiler or heat pump short cycling if the have a thermostat on each loop. Been there and then removed and simplified, after I saw my first months gas usage. If I was you I would have a single zone and use the bedroom stats as limit stops (balance flow to get the temperature correct). Join all other loops to operate off a single thermostat. Link to comment Share on other sites More sharing options...
dave1967 Posted August 28, 2022 Author Share Posted August 28, 2022 Why wouldn't you use one stat per port. I was under the impression you could then control each zone / room independently. Link to comment Share on other sites More sharing options...
dave1967 Posted August 28, 2022 Author Share Posted August 28, 2022 Cheers for the replys. It for a rad system. Decided against underfloor heating. Link to comment Share on other sites More sharing options...
JohnMo Posted August 28, 2022 Share Posted August 28, 2022 You can control each one individually, but your boiler will only have limited turndown, so if the minimum turndown is 4kW and a single circuit or zone calls for heat that can only absorb 1kW, the boiler cannot get the heat away quick enough. It will trip when the return temperature is too high. This will lead to a 10min or so outage while the boiler goes through a reset cycle. This will keep repeating until more circuits come back online. This is the least efficient way to run your boiler. And will result in much bigger fuel usage. Link to comment Share on other sites More sharing options...
dave1967 Posted August 28, 2022 Author Share Posted August 28, 2022 Cheers for the info John. Link to comment Share on other sites More sharing options...
Alexphd1 Posted August 29, 2022 Share Posted August 29, 2022 We are running our upstairs radiators on a ufh manifold but this is being feed of a buffer tank. Link to comment Share on other sites More sharing options...