Hi All,
I have completed my heat loss calcs for my new-build using Jeremy's spreadsheet (many thanks Jeremy!) however I would like a little help in interpreting the results please.
From the spreadsheet I am hoping to size an ASHP, which will be the only source of heating for the house expect 2 x log-burners.  (Note: there is no mains gas to the property).
Any help in interpreting the results as well as a sense-check on the figures used would be gratefully received.
Kind Regards,
Steve.
Heat loss calculator - Hereford House.xlsxFetching info...
I would work on the figure in G 65, heat loss at 25 degrees delta t.  assuming you want the house at 20 degrees and it rarely gets below -5 where you are, that will be the worst case heat load on the coldest day you are likely to get.
So that's a figure of 9883W
Now you won't want the ASHP running 24/7 and in any case it will spend some time heating DHW so I would be looking at a minimum of a 15kW ASHP
Now go and tweak U values and see how much better you can get that figure.
For a comparison, I used the figure in H 65 as -10 outside is not uncommon here and my heat loss there is just under 2,5kW
Expand
Thanks for your reply.
There were a couple of parameters that made a big difference to the heat loss, those being; air changes per hour and MVHR efficiency.  I set the ACH to 3 as I think this refers to the leakage through the building fabric?  If this is correct, I believe 3 ACH is achievable, and maybe I can improve on this through some of the advice I have recently read on this forum.  Having spoken with the guys that will be completing my air-testing they have advised that a wet plaster will certainly help with leakage so this is a route I will take.
Unfortunately the insulation is already fitted in the floors and in the walls, however I am trying to improve the U-values for the roof as the insulation is yet to be fitted here!
Expand
Think you might be confusing units...
I think the recommended level of air tightness on a pressure test is ideally below 3 m3/(m2*h) measured at some pressure which I forget.
The ACH figure is what your MVHR is designed and set to deliver. I think its normally less than 1ACH. Passive houses 0.7 ACH I think? So I think you have it set too high in the spreadsheet.
Someone else can correct me if I have those numbers wrong.
Expand
Thanks for the reply.
I will adjust as ACH to <1, but where do I enter the “leakiness” of my property please? :)