Heat Loss Calcs - Interpretation (to help size an ASHP)

Featured Replies

Hi All,

 

I have completed my heat loss calcs for my new-build using Jeremy's spreadsheet (many thanks Jeremy!) however I would like a little help in interpreting the results please.

 

From the spreadsheet I am hoping to size an ASHP, which will be the only source of heating for the house expect 2 x log-burners.  (Note: there is no mains gas to the property).

 

Any help in interpreting the results as well as a sense-check on the figures used would be gratefully received.

 

Kind Regards,

Steve.

 

 

Heat loss calculator - Hereford House.xlsx

I would work on the figure in G 65, heat loss at 25 degrees delta t.  assuming you want the house at 20 degrees and it rarely gets below -5 where you are, that will be the worst case heat load on the coldest day you are likely to get.

 

So that's a figure of 9883W

 

Now you won't want the ASHP running 24/7 and in any case it will spend some time heating DHW so I would be looking at a minimum of a 15kW ASHP

 

Now go and tweak U values and see how much better you can get that figure.

 

For a comparison, I used the figure in H 65 as -10 outside is not uncommon here and my heat loss there is just under 2,5kW

  • Author
28 minutes ago, ProDave said:

I would work on the figure in G 65, heat loss at 25 degrees delta t.  assuming you want the house at 20 degrees and it rarely gets below -5 where you are, that will be the worst case heat load on the coldest day you are likely to get.

 

So that's a figure of 9883W

 

Now you won't want the ASHP running 24/7 and in any case it will spend some time heating DHW so I would be looking at a minimum of a 15kW ASHP

 

Now go and tweak U values and see how much better you can get that figure.

 

For a comparison, I used the figure in H 65 as -10 outside is not uncommon here and my heat loss there is just under 2,5kW

 

Thanks for your reply.

 

There were a couple of parameters that made a big difference to the heat loss, those being; air changes per hour and MVHR efficiency.  I set the ACH to 3 as I think this refers to the leakage through the building fabric?  If this is correct, I believe 3 ACH is achievable, and maybe I can improve on this through some of the advice I have recently read on this forum.  Having spoken with the guys that will be completing my air-testing they have advised that a wet plaster will certainly help with leakage so this is a route I will take.

 

Unfortunately the insulation is already fitted in the floors and in the walls, however I am trying to improve the U-values for the roof as the insulation is yet to be fitted here!

1 hour ago, F113tch said:

 I set the ACH to 3 as I think this refers to the leakage through the building fabric? 

 

Think you might be confusing units...

 

I think the recommended level of air tightness on a pressure test is ideally below 3 m3/(m2*h) measured at some pressure which I forget.

 

The ACH figure is what your MVHR is designed and set to deliver. I think its normally less than 1ACH. Passive houses 0.7 ACH I think? So I think you have it set too high in the spreadsheet.

 

Someone else can correct me if I have those numbers wrong.

 

  • Author
10 hours ago, Temp said:

 

Think you might be confusing units...

 

I think the recommended level of air tightness on a pressure test is ideally below 3 m3/(m2*h) measured at some pressure which I forget.

 

The ACH figure is what your MVHR is designed and set to deliver. I think its normally less than 1ACH. Passive houses 0.7 ACH I think? So I think you have it set too high in the spreadsheet.

 

Someone else can correct me if I have those numbers wrong.

 

 

Thanks for the reply.

 

I will adjust as ACH to <1, but where do I enter the “leakiness” of my property please? :)

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.