Second DPC at external door openings


WWilts

Recommended Posts

43 minutes ago, WWilts said:

"DPCs to be set at least 150mm above external ground level and second DPC to be set 150mm above this to 900mm either side of entrance door accesses."

Why is this second higher DPC specified on either side of external doors?

Because DPC should be at least 150mm above ground level & the assumption is made that your entrance will be a ‘level threshold’ (level-ish with your internal finished floor level to allow wheelchair access) and therefore a secondary DPC is required in this zone to prevent rainwater splash up saturating the superstructure wall. This secondary dpc should extend the specified distance past the raised ground level & then step down to lap into the lower dpc. 

  • Like 2
Link to comment
Share on other sites

1 hour ago, Brickie said:

prevent rainwater splash up saturating the superstructure wall. This secondary dpc should extend the specified distance past the raised ground level & then step down to lap into the lower dpc. 

Is this second DPC on the outer leaf only?

Link to comment
Share on other sites

33 minutes ago, WWilts said:

s this second DPC on the outer leaf only?

Yes. 
It’s only a cavity tray if it’s described as such,and would continue around the perimeter of the build,and would also normally lap out at at finished floor level (I.e. the standard DPC height.)

  • Like 1
Link to comment
Share on other sites

4 hours ago, Brickie said:

That is a Cavity Tray,yes,though it would normally be lapped out FFL. Is this your own drawing or one you were supplied with?

Own drawing, tweaked another.

 

Not familiar with the term lapped out. Does the pic now show lapping out? Sorry to be so ignorant.

Splash dpc entrances lapped.jpg

Link to comment
Share on other sites

I’m referring to the positioning of the tray in terms of coursing,as you look at your drawing. The height of the lower (outer) part of the tray would usually be at DPC level (which is usually the same as FFL.) If it helps,visualise the substructure walls all built up to the height of the (as yet uninstalled) finished floor. Now,one course of blocks is laid on the inner skin, the tray is installed and lapped out & down so going from DPC plus 225mm internally to DPC height externally. 

  • Like 1
Link to comment
Share on other sites

  • 6 months later...

Anyone know if the recommended 150mm distance can be reduced when there is a french drain immediately next to the external face of the wall, such that rainwater shouldn't splash as high as 150mm because it is hitting gravel in the french drain?