March 25, 20215 yr So daughter phones (again) Dad, my electrics is tripping, if i leave it off for 10 mins then i can flick the rcd back on and it will last 10 mins before tripping again. So off i trot. I won't go through all the testing this and that but, finally removed some boxing around the boiler, and found the wire providing power to the boiler wrapped around the heating flow pipe. Well you can guess the rest but sorted now. fingers crossed that was the only problem for a while.
March 25, 20215 yr 5 hours ago, Big Jimbo said: So daughter phones (again) Dad, my electrics is tripping, if i leave it off for 10 mins then i can flick the rcd back on and it will last 10 mins before tripping again. So off i trot. I won't go through all the testing this and that but, finally removed some boxing around the boiler, and found the wire providing power to the boiler wrapped around the heating flow pipe. Well you can guess the rest but sorted now. fingers crossed that was the only problem for a while. Been there . My daughter “ tv doesn’t work , microwave doesn’t work , oh lights don’t work “ Flick magic consumer unit switch love ! . Fixed !
March 25, 20215 yr It does highlight the benefit to have an all RCBO cu. Having the "boiler" on it's own circuit would narrow it down very quickly. Even to the point of the person "phoning" can easily convey what circuit is tripping.
March 25, 20215 yr 1 hour ago, Onoff said: It does highlight the benefit to have an all RCBO cu. Having the "boiler" on it's own circuit would narrow it down very quickly. Even to the point of the person "phoning" can easily convey what circuit is tripping. Totally agree- minimising grief, good design