Joe87 Posted September 16, 2020 Share Posted September 16, 2020 (edited) Hi all, I have a 4 meter opening in a garden room I've built for some bifolds but need a lintel above to stop deflection of the doors. Which lintel would be best for a single skin dense concrete block wall though? Above the door maybe a course of dense concrete blocks and then a warm flat roof over the whole thing. Building the walls was fairly straight forward but lintels seem to be a minefield. There seems to be so many types. Thanks for any help Joe Edited September 16, 2020 by Joe87 Link to comment Share on other sites More sharing options...
nod Posted September 16, 2020 Share Posted September 16, 2020 14 minutes ago, Joe87 said: Hi all, I have a 4 meter opening in a garden room I've built for some bifolds but need a lintel above to stop deflection of the doors. Which lintel would be best for a single skin dense concrete block wall though? Above the door maybe a course of dense concrete blocks and then a warm flat roof over the whole thing. Building the walls was fairly straight forward but lintels seem to be a minefield. There seems to be so many types. Thanks for any help Joe I wouldn’t use a thing other than steel With steel prices so low there isn’t a massive difference A 5 mill drop above the bigolds will cause them not to open Link to comment Share on other sites More sharing options...
Joe87 Posted September 16, 2020 Author Share Posted September 16, 2020 1 hour ago, nod said: I wouldn’t use a thing other than steel With steel prices so low there isn’t a massive difference A 5 mill drop above the bigolds will cause them not to open What type of lintel would you think best? Something like an I beam or is there another type better suited do you know? Also if I did use an I beam, do I simply put a bed of mortar directly on top of the steel and then put another course of bricks to finish of the wall? Thanks for the reply. Link to comment Share on other sites More sharing options...
PeterW Posted September 16, 2020 Share Posted September 16, 2020 How are you planning on insulating this room ..? That will have a bearing on the beam type and also the lintel construction method 1 Link to comment Share on other sites More sharing options...
Mr Punter Posted September 16, 2020 Share Posted September 16, 2020 If it is exposed it would be best galvanised. A Universal Beam (UB) would be most common. You will need advice from someone on the section size. Link to comment Share on other sites More sharing options...
Joe87 Posted September 16, 2020 Author Share Posted September 16, 2020 17 minutes ago, PeterW said: How are you planning on insulating this room ..? That will have a bearing on the beam type and also the lintel construction method I planned on a timber frame inside with insulation board and plastering to finish it all off. 17 minutes ago, Mr Punter said: If it is exposed it would be best galvanised. A Universal Beam (UB) would be most common. You will need advice from someone on the section size. I was told the same thing by someone else that I could use a UB but just wanted to be sure here before I went ahead and made a mistake. The opening is about 4 meters and it won't really be holding much weight above. Just a flat roof. So nothing extreme like a second floor or anything. Link to comment Share on other sites More sharing options...
nod Posted September 16, 2020 Share Posted September 16, 2020 The problem you have with lintels If there’s not much above them they are likely to move Anything over 2ntrs I used a steel with a hit and mis plate For one skin a steel is perfect Especially with bifold This is one of three that I’ve just fitted 1 Link to comment Share on other sites More sharing options...
MikeGrahamT21 Posted September 16, 2020 Share Posted September 16, 2020 IG do a free design service if you send them specs of your building, they'll run calculations and specify a lintel for the job, i've used it before, and it was pretty quick 1 Link to comment Share on other sites More sharing options...
PeterW Posted September 16, 2020 Share Posted September 16, 2020 49 minutes ago, Joe87 said: I planned on a timber frame inside with insulation board and plastering to finish it all off. I was told the same thing by someone else that I could use a UB but just wanted to be sure here before I went ahead and made a mistake. The opening is about 4 meters and it won't really be holding much weight above. Just a flat roof. So nothing extreme like a second floor or anything. OK so which way do the roof joists run ..?? If they land on the lintel then there is a huge load, if they are parallel then the load is negligible. That affects the size of the beam. Link to comment Share on other sites More sharing options...
nod Posted September 16, 2020 Share Posted September 16, 2020 16 minutes ago, PeterW said: OK so which way do the roof joists run ..?? If they land on the lintel then there is a huge load, if they are parallel then the load is negligible. That affects the size of the beam. If you ask a SE He will tell a low amount of weight isn’t good Lintels rely on weight to keep everything in place We have a flat roof and a metre of double skinned block above our orangery SE still class it as low weight and not suitable for catnics etc Link to comment Share on other sites More sharing options...
PeterW Posted September 16, 2020 Share Posted September 16, 2020 Yep hence why I said beam size as lintels to 4m length really don’t exist in single skin. I agree with @nod that you need an SE to design this as it needs to be stiff enough to both resist bending and also resist twisting over that length. Link to comment Share on other sites More sharing options...
Mr Punter Posted September 16, 2020 Share Posted September 16, 2020 End bearings for steels are also important. Normally concrete padstones but sometimes steel posts are required. Link to comment Share on other sites More sharing options...
Joe87 Posted September 16, 2020 Author Share Posted September 16, 2020 7 hours ago, PeterW said: OK so which way do the roof joists run ..?? If they land on the lintel then there is a huge load, if they are parallel then the load is negligible. That affects the size of the beam. The roof joists would be running away from the lintel not across it. So if the lintel is left to right then the joists would run backwards from it. I did forget to say aswell that the opening has an end pier on each side of it. So two dense concrete blocks laying face down and then two side by side to make the end pier. So the area the lintel would rest on would be about 215mm rather then the 100mm of the block edge. I hope that makes sence, my explaining of these things is not great. 7 hours ago, nod said: The problem you have with lintels If there’s not much above them they are likely to move Anything over 2ntrs I used a steel with a hit and mis plate For one skin a steel is perfect Especially with bifold This is one of three that I’ve just fitted How big was this opening Nod in the image? It looks good. Do you have an example of what you would use over a 4 meter span, like a website link or something? Sorry to be a pain. Thanks! I appreciate the help Link to comment Share on other sites More sharing options...
Mr Punter Posted September 16, 2020 Share Posted September 16, 2020 Just phone or email a couple of structural engineers for a quote to size the steel and spec the bearings. You will need drawings, including the roof makeup. The cost is v. low. They will spec something that will work without being heavier than needed, which will be far better when it comes to installing it. 1 Link to comment Share on other sites More sharing options...
nod Posted September 16, 2020 Share Posted September 16, 2020 1 hour ago, Joe87 said: The roof joists would be running away from the lintel not across it. So if the lintel is left to right then the joists would run backwards from it. I did forget to say aswell that the opening has an end pier on each side of it. So two dense concrete blocks laying face down and then two side by side to make the end pier. So the area the lintel would rest on would be about 215mm rather then the 100mm of the block edge. I hope that makes sence, my explaining of these things is not great. How big was this opening Nod in the image? It looks good. Do you have an example of what you would use over a 4 meter span, like a website link or something? Sorry to be a pain. Thanks! I appreciate the help 4 mtr Link to comment Share on other sites More sharing options...
nod Posted September 16, 2020 Share Posted September 16, 2020 1 hour ago, Joe87 said: The roof joists would be running away from the lintel not across it. So if the lintel is left to right then the joists would run backwards from it. I did forget to say aswell that the opening has an end pier on each side of it. So two dense concrete blocks laying face down and then two side by side to make the end pier. So the area the lintel would rest on would be about 215mm rather then the 100mm of the block edge. I hope that makes sence, my explaining of these things is not great. How big was this opening Nod in the image? It looks good. Do you have an example of what you would use over a 4 meter span, like a website link or something? Sorry to be a pain. Thanks! I appreciate the help The handy thing I find with a steel is that you can jack the frame up tight against the underside and know it will never move The four that we fitted a few weeks back and the one on my house have no adjustment So you are relying on Toe and healing the glass Any movement and the doors won’t open Our structural engineer refers to lintels as his bread and butter jobs and hates any lintel over 2000 mil 1 Link to comment Share on other sites More sharing options...
Joe87 Posted September 17, 2020 Author Share Posted September 17, 2020 10 hours ago, nod said: The handy thing I find with a steel is that you can jack the frame up tight against the underside and know it will never move The four that we fitted a few weeks back and the one on my house have no adjustment So you are relying on Toe and healing the glass Any movement and the doors won’t open Our structural engineer refers to lintels as his bread and butter jobs and hates any lintel over 2000 mil Thanks nod. So what I'm looking for is a steel (by this do you mean a universal beam?) with a hit and miss plate. I'm glad to hear you have done so many. Link to comment Share on other sites More sharing options...
nod Posted September 17, 2020 Share Posted September 17, 2020 19 minutes ago, Joe87 said: Thanks nod. So what I'm looking for is a steel (by this do you mean a universal beam?) with a hit and miss plate. I'm glad to hear you have done so many. If you are single skin brick or block an Straight forward RSJ will be fine If double Skin a welded plate is added to the underside to carry the second skin You will be suprised how little difference there is in price between a Rsj and a good quality lintel Once the beam is in you can forget about it and will give you a solid fixing points 1 Link to comment Share on other sites More sharing options...