epsilonGreedy Posted July 21, 2020 Share Posted July 21, 2020 According to my maths the answer is 16.6 tons which is just silly. Could someone spot the error in the following arithmetic? A 3.7N rated block should cope with a compressive load of 3.7N per mm squared. The surface area of a standard 100mm wide block is 100mm x 440mm = 44,000 mm squared. Therefore a block can support 44,000 x 3.7N = 162,800N before it is at risk of crumbling under the total load above. There are 9.8N in a Kg* which means a block can support 162,800 / 9.8N = 16.6 tons. * For the scientifically pedantic this might not apply in Cornwall or on Planet @SteamyTea. Link to comment Share on other sites More sharing options...
Mr Punter Posted July 21, 2020 Share Posted July 21, 2020 But when you run over them with a telehandler they crumble to dust. Link to comment Share on other sites More sharing options...
Temp Posted July 21, 2020 Share Posted July 21, 2020 Calculations look right to me. I believe you need to reduce the result by a safety margin. Factor of 2? I think the compressive strength of blocks is mainly a concern where you have beams and lintels that concentrate loads onto the bearing ends. I'm not an SE though. Link to comment Share on other sites More sharing options...
epsilonGreedy Posted July 22, 2020 Author Share Posted July 22, 2020 20 hours ago, Temp said: Calculations look right to me. I believe you need to reduce the result by a safety margin. Factor of 2? I think the compressive strength of blocks is mainly a concern where you have beams and lintels that concentrate loads onto the bearing ends. I was thinking about the inner block wall that contributes to supporting a 1.8m all chimney on a hipped roof. The corbeled plinth for this is built over three blocks and I reckon it takes about 500Kg of the total 780Kg weight of the chimney when wind pressure is zero. If my calculation of 16.6 tons per 3.7N block is correct, then my 780kg chimney is many factors within the 50 ton support limit of those 3 blocks even allowing +10% for a rain sodden chimney and wind pressure. I still like the idea of enhancing the lateral stability of the block wall with 12mm cement board like Hardiebacker. Link to comment Share on other sites More sharing options...
Temp Posted July 22, 2020 Share Posted July 22, 2020 I'd take advice from an SE. I really don't like the idea of using hardibacker board for this! Our SE specified 7N blocks with 14N blocks for our chimney and some pillars because we have a beam and block first floor. Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now