Dreadnaught Posted January 16, 2020 Share Posted January 16, 2020 Basic question if I may. Anyone with an MBC-style raft will be able to answer in a flash I expect. With an insulated reinforced concrete raft foundation (200mm concrete over EPS), how does a conduit run to a kitchen island (or, for example, to floor sockets in the sitting area) for electrical cabling? Possible answer 1: does the conduit penetrate all the way through the raft and the EPS into the soil beneath, like a service penetration, and then re-emerge elsewhere in the build next to a wall? Possible answer 2: does the conduit penetrate laterally throughs the raft spanning from a wall to the island without penetrating the EPS? Link to comment Share on other sites More sharing options...
Jeremy Harris Posted January 16, 2020 Share Posted January 16, 2020 I just ran 25mm electrical conduit through the slab like this, with gentle bends on either end to make it easier to pull the cables through: Before the pour, the conduit was cable tied to the steel mesh to hold it in position. 1 Link to comment Share on other sites More sharing options...
RandAbuild Posted January 16, 2020 Share Posted January 16, 2020 Don't forget about drainage & water if you're thinking about having a sink on the island too 1 Link to comment Share on other sites More sharing options...
RandAbuild Posted January 16, 2020 Share Posted January 16, 2020 Here's ours 1 Link to comment Share on other sites More sharing options...
Carrerahill Posted January 16, 2020 Share Posted January 16, 2020 27 minutes ago, Dreadnaught said: Possible answer 1: does the conduit penetrate all the way through the raft and the EPS into the soil beneath, like a service penetration, and then re-emerge elsewhere in the build next to a wall? It would not go through the lot to the soil no, it depends on makeup of your slab and all sorts but it could be encased in the concrete, the big house builders tend only to put the bare minimal in the slab like incoming utilities and drainage, then all the wiring and radiator pipes drops from the ceiling level, I don't like this way much but as an example it's what some do. There are so many ways to do this to be honest. 1 Link to comment Share on other sites More sharing options...
Dreadnaught Posted January 16, 2020 Author Share Posted January 16, 2020 (edited) 20 minutes ago, RandAbuild said: Here's ours Oh, is that image in preparation for the pour of a screed? Edited January 16, 2020 by Dreadnaught Link to comment Share on other sites More sharing options...
Dreadnaught Posted January 16, 2020 Author Share Posted January 16, 2020 32 minutes ago, Jeremy Harris said: I just ran 25mm electrical conduit through the slab like this, with gentle bends on either end to make it easier to pull the cables through: Thanks @Jeremy Harris. The other end seems to come up in your double-stud wall. Am I right? Why was that? Link to comment Share on other sites More sharing options...
Jeremy Harris Posted January 16, 2020 Share Posted January 16, 2020 4 minutes ago, Dreadnaught said: Thanks @Jeremy Harris. The other end seems to come up in your double-stud wall. Am I right? Why was that? The wall end of the conduit comes up inside the service void, just inside the twin stud wall, and the cables then run vertically up to the isolator switches on the wall above. 1 Link to comment Share on other sites More sharing options...
RandAbuild Posted January 16, 2020 Share Posted January 16, 2020 (edited) 8 minutes ago, Dreadnaught said: Oh, is that image in preparation for the pour of a screed? Yes, that's before the final screed. We did not have an MBC insulated slab though. Ours was a 'Jetfloor ' - insulated blocks between concrete beams, overlaid with EPS. The drainage was laid below the Jetfloor (as in a traditional block and beam), but the services were in the screed (including supply for our induction hob). If you have a sink in your island, I presume your drainage would be the same as foul drains below the MBC slab? [You can see we also added a gas supply in case we didn't like the induction hob (we do!)] Edited January 16, 2020 by RandAbuild Additional text added 1 Link to comment Share on other sites More sharing options...
PeterW Posted January 16, 2020 Share Posted January 16, 2020 I use 32mm solvent weld pipe and a pair of 45 degree bends on each end. Makes it easier to thread 10mm cable through as it can be very stiff. Bring it a fair bit higher than the slab and then just cap it off both ends so it doesn’t get filled with water or concrete. 1 Link to comment Share on other sites More sharing options...
Dreadnaught Posted January 16, 2020 Author Share Posted January 16, 2020 Thanks all. Makes sense. Want to have floor sockets under the sofas for table lamps. That will need a conduit as you all describe. But what about a former in the concrete for the actual socket in the floor? Link to comment Share on other sites More sharing options...