Alexphd1 Posted October 23, 2018 Share Posted October 23, 2018 (edited) Can I run solar DC cable in same trunking as normal 240v AC cable? Edited October 23, 2018 by Alexphd1 Link to comment Share on other sites More sharing options...
Onoff Posted October 23, 2018 Share Posted October 23, 2018 You need to physically separate them. See the commissioning sheets tick box. Not sure if this is the latest: Guide_to_the_installation_of_PV_systems_2nd_Edition.pdf Link to comment Share on other sites More sharing options...
Alexphd1 Posted October 23, 2018 Author Share Posted October 23, 2018 bugger Link to comment Share on other sites More sharing options...
Nickfromwales Posted October 23, 2018 Share Posted October 23, 2018 Most runs I’ve seen have been segregated, but they have mostly been retro fits. Just wondering if EMF off the A/C side ( constant ) would affect the D/C side. Link to comment Share on other sites More sharing options...
Onoff Posted October 23, 2018 Share Posted October 23, 2018 44 minutes ago, Nickfromwales said: Most runs I’ve seen have been segregated, but they have mostly been retro fits. Just wondering if EMF off the A/C side ( constant ) would affect the D/C side. Potentially yes. I guess if it's a long run and they're dead parallel, v.unlikely in reality as cables get a bit of a natural twist. Trunking inside trunking or flex conduit inside trunking? That'd tick the separation box. Link to comment Share on other sites More sharing options...
Alexphd1 Posted October 23, 2018 Author Share Posted October 23, 2018 Much appreciated. Will run a extra trunking tomorrow. Link to comment Share on other sites More sharing options...