Filling pipes & risk of freezing in insulated raft.

Featured Replies

Opinions/advise please on a few things:

  1. Should we fill/pressurise pipes before the concrete pour?

    I know general advice is yes, fill them but, seem to recall some saying no need to bother (feels risky though!)

  2. If we fill them then, given its almost December and unlikely we will have any frost protection for some time, what's the best approach?

    Add glycol (no idea how much or how - assume mix with water then pump in together) How best to protect exposed tail ends & the manifold?

  3. Can anyone advise/have ideas on how we can support the manifold on top of the raft before the pour? It's not going to be on an outside wall but will only be about a metre in so possibly could put a support arm across.

    ?building a frame? Anyone got any pics of ones they've made?

TIA 🙃

See the top of this picture. A plank attached to two starter bars ( right angled rebar tied to the mesh). You can cut off the excess bar later if not required.

20210827_175916.jpg

Given your other post about a few areas having less than ideal concrete cover, I would suggest you fill the system.

There will be loads of people tell you that you don’t need to fill, and then you don’t need to fill with EG if you do fill. That may be true in most instances, but for ours, it wasn’t the place I wanted to gamble. So we filled with an EG mix, filled with gravity after purging.

We filled with water and added glycol to protect down to -10 (filled in Nov). The other option is pressure with compressed air. Then there is no freeze risk and the pipes aren't going to be crushed.

We supported the UFH manifold on a plywood stand, cast it into the concrete and that is how it is still supported (intended to that way)

Fill with water/pressurise shortly before the pour. The concrete curing heat will keep the water from freezing while the concrete cures and you shouldn't really pour concrete if it's freezing anyway.

After the initial cure while there is still a little warmth use compressed air to blow out the bulk of water and then pressurise with air. (Pressurising with air is not advisable during the pour - though some do it - check the safety issues).

That way you don't have to worry about water freezing after the initial pour. Yes, using compressed air won't get rid of all the water in the pipes but so long as there is air space in the pipes (air compresses) there should be room for any freezing water to expand into.

You could skip the pressurise with air step if you want, but it's likely still good to have a way to monitoring the pipework over time as people move about on site/may need to drill into the slab.

You would obviously need an air compressor for this method but small ones aren't hugely expensive.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.