Rationel Window - Water Ingress- Help!

Featured Replies

Hi Everyone

Desperate for some advice on a bit of water ingress coming in at floor level cill during heavy rain.

We had Rationel windows installed as part of our timber frame contract. They have been fine generally but one tall fixed light widow has a small amount of water ingress. I have tried adding CT-1 in a few places but the problem persists. The walls have been clad externally with fibre cement board and then rendered with Baumit Silikontop. The walls have now been plasterboarded and skimmed ....then the problem came back when it rained. I have been racking my brain trying to figure out how the water is getting in so any advice would be most welcome.

Here's the detail from Rationel with my notes added:

image.png

Here are some photos of the current situation:

Internally damp patches showing through the levelling compound and external view of cill

IMG_20261118_114848165.jpgIMG_20261118_114850698.jpgIMG_20261118_114926853_HDR.jpg

Here's a 3D of the detail...

image.png

What can I do, preferably without ripping of the render and boarding to investigate?

3 hours ago, Stratman said:

What can I do, preferably without ripping of the render and boarding to investigate?

I have had the same problem in the past. It was caused by wind driven rain being forced through the small gap, shown by red arrow, when the sealant wasn't fitted properly. Is the leak only when the wind is in one direction? Pack the gap in the corner with something waterproof and removable, such as a piece of closed cell foam, to check the cause. It can be filled permanently with CT1 well masked.

image.thumb.png.1c6967bedc277d569944a519d19b6461.png

Edited by Gone West

I'd email your photos to Rationel and ask their advice.

It's hard to tell from your picture but I wonder if the sealant between the cill and the bottom of the frame may be too far forward? In the detail it's sealing the cill to the wooden frame, but yours looks like it may be sealing the cill to the aluminium cladding in front - if a bit of moisture gets behind that then it's got to go somewhere and that won't be through the bottom onto the cill

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.