Approach to rectifying screed height mismatch

Featured Replies

Morning,

We have converted a conservatory area into what I would call a normal room, with a TF extension which was built off of existing foundations as they were deemed adequate enough. We also retained the ground bearing slab, 100mm PIR and traditional screed with UFH.

With the wall now out, its apparent that what was the conservatory screed is circa 25-30mm lower than the kitchen screed across the floor - measured using laser a measuring stick.

Where the wall has come out, circa 250mm gap, the DPMs have been joined up to be continuous across the gap and so far, 50mm of PIR has been laid. Could maybe getaway with another 25mm, but cannot match to the PIR in the kitchen because of the height difference and would leave screed thin in that area.

Conservatory area screed has 25mm PIR and a 10mm foam expansion strip around its perimeter, which finishes at the height of the screed. Unfortunately the polythene slip sheet is not present all the way around. Looks like someone has previously gone round and torn it out once the screed was dry when done originally. Eg, may removing excess, I dont know........

Contractor 1 - advised optimal solution would be to screed the wall gap to the height of existing conservatory screed then use a self levelling compound to required height. However, in their view, there is currently no way to contain the self levelling compound from draining down the sides at the perimeter, as this would usually be done by membrane/ slip sheet being brought up the sides. Bonded screed was a no as new layer too thin and heated screed below would cause it to fail.

Contractor 2 - Remove the old screed and start again, but stating this may damage the UFH pipes.

Is there a way to re-do the perimeter side of things to make it liquid proof and hold in the self levelling? Or should I bite the bullet and careful remove the old screed - about 23 Sqm of it.

Thoughts / advise welcomed.

John

  • Author
3 hours ago, crispy_wafer said:

create a dam with expanding foam all round the perimeter?

I have attached a photo of one section of perimeter to show what I have in situ.

The contractor was advising there needs to be a new upstand to contain the self levelling, so I am wondering if I can work around the perimeter putting a new foam upstand in and then somehow silicone/stick it to the outside of the existing screed edge to form a watertight seal.

Perimeter Picture.jpeg

Hi John, I wouldn't rip out 23 sqm of heated screed for 25 to 30mm. That's well within what a decent fibre reinforced levelling compound rated for underfloor heating can do, and those are designed to bond to the screed rather than float on a slip sheet, so the missing polythene isn't the problem it sounds.

Roughly how I'd go about it:

  • Heating off a couple of days beforehand, and grind or sand off any laitance, dust and old adhesive so you're onto sound screed.

  • Perimeter: cut the old foam strip down a few mm, fill any gaps or voids at the edge with foam and trim it back, then stick a self adhesive edge strip with a film tail round the walls, standing above finished level. Run a bead of sealant where it meets the wall and the screed and tape the tail down. That holds the compound in fine.

  • Timber battens as temporary dams at doorways, and across the old wall line if you do it in sections.

  • Prime with the compound maker's own primer, then pour to the depth they allow. Some need a second lift or added aggregate above 10 to 15mm, so check the data sheet for 30mm.

  • Leave the heating off until it's fully cured, then bring it up slowly over a week or so.

Worth looking at the floor finish build up in each room too, as a thinner finish in that room might save you a few mm.

Get a couple of cans of illbruck fm330 and fill that perimeter gap, when it is hard trim it off, then you can floor level over the whole area.

  • Author
On 14/11/2026 at 10:18, JpManning said:

Hi John, I wouldn't rip out 23 sqm of heated screed for 25 to 30mm. That's well within what a decent fibre reinforced levelling compound rated for underfloor heating can do, and those are designed to bond to the screed rather than float on a slip sheet, so the missing polythene isn't the problem it sounds.

Roughly how I'd go about it:

  • Heating off a couple of days beforehand, and grind or sand off any laitance, dust and old adhesive so you're onto sound screed.

  • Perimeter: cut the old foam strip down a few mm, fill any gaps or voids at the edge with foam and trim it back, then stick a self adhesive edge strip with a film tail round the walls, standing above finished level. Run a bead of sealant where it meets the wall and the screed and tape the tail down. That holds the compound in fine.

  • Timber battens as temporary dams at doorways, and across the old wall line if you do it in sections.

  • Prime with the compound maker's own primer, then pour to the depth they allow. Some need a second lift or added aggregate above 10 to 15mm, so check the data sheet for 30mm.

  • Leave the heating off until it's fully cured, then bring it up slowly over a week or so.

Worth looking at the floor finish build up in each room too, as a thinner finish in that room might save you a few mm.

Many thanks for the detailed reply. Those ideas will work for the majority to the perimeter, and should be easily doable.

There is old adhesive on there, so looks like I will need some sort of floor grinder hired.

The bits I think may be more problematic, are the section where the old wall was and where the new sliding door now is.

The kitchen floor is also finished already and we had not planned to mess with that. Eg idea was to align new bit with kitchen. Half of the join will be covered with units. The open joint we were going to use an expansion strip / tile joint strip to transition from one floor to the other.

Door side:

Where the sliding door is now, was a wall and this had the same blue foam strip, then 25mm PIR in there, which got removed. There is then a circa 15mm gap from behind the foam upstand where it abuts the blockwork, back to the door threshold. This is essentially where the door sits on the blockwork. It finishes 15mm back from the block face.

My original idea was to push the bluefoam upstand back against the door threshold then fill with new screed to existing level, then poor 30mm layer. Its this section that concerned the screeding contractors. Too narrow to screed it apparently - eg not enough mass to keep it in situ and would come away at the point it joins the old screed. I did suggest putting the foam back in and sealing, then pouring new layer, but they felt as it was a tread area next to the door, that wouldn't be suitable and 30mm over PIR bit would crack where it met the old screed. This is when we got into the realms of screed removal so as to allow this section to be done properly with the rest of the floor as one.

Could one cut out say a 4m x 0.5m area which would then allow for a new section of screed to be done up to the door, let that dry out, then pour 30mm top up layer after?

Old wall section:

This is differing in width as nearest part in the pic was a sliding door sat on outer leaf, and B&B/PIR/screed in kitchen was taken up to that and then the further part was double skin with a window in it. I assume this should be traditional screeded first, maybe with some polymer additives and fibres to strengthen. Do that to the height of the old screed, then get the poured 30mm layer done over the lot.

Further thoughts welcomed

Door side.jpeg

wall removed area.jpeg

15 hours ago, john0wingnut said:

Many thanks for the detailed reply. Those ideas will work for the majority to the perimeter, and should be easily doable.

There is old adhesive on there, so looks like I will need some sort of floor grinder hired.

The bits I think may be more problematic, are the section where the old wall was and where the new sliding door now is.

The kitchen floor is also finished already and we had not planned to mess with that. Eg idea was to align new bit with kitchen. Half of the join will be covered with units. The open joint we were going to use an expansion strip / tile joint strip to transition from one floor to the other.

Door side:

Where the sliding door is now, was a wall and this had the same blue foam strip, then 25mm PIR in there, which got removed. There is then a circa 15mm gap from behind the foam upstand where it abuts the blockwork, back to the door threshold. This is essentially where the door sits on the blockwork. It finishes 15mm back from the block face.

My original idea was to push the bluefoam upstand back against the door threshold then fill with new screed to existing level, then poor 30mm layer. Its this section that concerned the screeding contractors. Too narrow to screed it apparently - eg not enough mass to keep it in situ and would come away at the point it joins the old screed. I did suggest putting the foam back in and sealing, then pouring new layer, but they felt as it was a tread area next to the door, that wouldn't be suitable and 30mm over PIR bit would crack where it met the old screed. This is when we got into the realms of screed removal so as to allow this section to be done properly with the rest of the floor as one.

Could one cut out say a 4m x 0.5m area which would then allow for a new section of screed to be done up to the door, let that dry out, then pour 30mm top up layer after?

Old wall section:

This is differing in width as nearest part in the pic was a sliding door sat on outer leaf, and B&B/PIR/screed in kitchen was taken up to that and then the further part was double skin with a window in it. I assume this should be traditional screeded first, maybe with some polymer additives and fibres to strengthen. Do that to the height of the old screed, then get the poured 30mm layer done over the lot.

Further thoughts welcomed

Door side.jpeg

wall removed area.jpeg

Hi John, on the door side I'd be wary of cutting a strip out. With heating in that screed you'd need to know exactly where the pipes run before a saw goes anywhere near it (heating on and a thermal camera shows them up well), and even then the new strip still meets the old screed at a joint, you've just moved it 500mm into the room. A lot of risk for not much gain.

Your contractors are right that a 15mm sliver of normal screed wont stay put, it hasn't got the body. But if that gap is sitting on the blockwork it doesn't need to be screed. I'd leave the blue foam upstand where it is against the old screed so the heated floor keeps its movement joint, then pack the gap between the foam and the threshold with a polymer modified repair mortar, primed with a bonding slurry first. Take it straight up to finished floor height, in a couple of layers if the bag says so. That gives you a solid strip on solid block under the door tread, and the compound then pours up to the foam like any other wall. Trim the foam flush after.

Old wall section, yes I'd do it the way you said. Sand and cement with fibres, bonded down with a slurry primer, brought up flush with the old screed and left to dry properly before the 30mm goes over the lot. Some people bed a strip of reinforcing scrim into the compound over the old and new joints too, cheap insurance on a heated floor

  • Author
On 19/11/2026 at 12:19, JpManning said:

Hi John, on the door side I'd be wary of cutting a strip out. With heating in that screed you'd need to know exactly where the pipes run before a saw goes anywhere near it (heating on and a thermal camera shows them up well), and even then the new strip still meets the old screed at a joint, you've just moved it 500mm into the room. A lot of risk for not much gain.

Your contractors are right that a 15mm sliver of normal screed wont stay put, it hasn't got the body. But if that gap is sitting on the blockwork it doesn't need to be screed. I'd leave the blue foam upstand where it is against the old screed so the heated floor keeps its movement joint, then pack the gap between the foam and the threshold with a polymer modified repair mortar, primed with a bonding slurry first. Take it straight up to finished floor height, in a couple of layers if the bag says so. That gives you a solid strip on solid block under the door tread, and the compound then pours up to the foam like any other wall. Trim the foam flush after.

Old wall section, yes I'd do it the way you said. Sand and cement with fibres, bonded down with a slurry primer, brought up flush with the old screed and left to dry properly before the 30mm goes over the lot. Some people bed a strip of reinforcing scrim into the compound over the old and new joints too, cheap insurance on a heated floor

Thanks for the reply.

On the door side, if I pack the 15/20mm area behind the foam with a polymer repair mortar, what do I put in the 20-25mm gap between the screed and the blue foam.

You can hopefully see in the pic where my hand is. The base of that gap has the underlying PIR that the old screed sits on.

So two bits to fill in that sense, or one if the blue foam is pushed back tight against the door.

John

4 hours ago, john0wingnut said:

Thanks for the reply.

On the door side, if I pack the 15/20mm area behind the foam with a polymer repair mortar, what do I put in the 20-25mm gap between the screed and the blue foam.

You can hopefully see in the pic where my hand is. The base of that gap has the underlying PIR that the old screed sits on.

So two bits to fill in that sense, or one if the blue foam is pushed back tight against the door.

John

Hi John, id put the foam tight against the old screed edge rather than pushing it back to the door. The old screed is the one with the heating in it so thats the bit that moves, and the movement joint wants to sit right up against it. If you fill between the old screed and the foam with mortar you've bonded a strip straight onto the heated screed with nothing to take the movement, and that's where it'll crack.

So you end up with just one strip between the foam and the threshold, roughly 35 to 45mm wide, part over the PIR and part on the blockwork. Pack the whole lot with the repair mortar so it's one solid piece, slurry primed onto the block and against the threshold. The bit sitting over the PIR is fine under foot traffic as it's narrow and keyed onto the block either side of it, PIR under a screed carries a lot more than that.

I wouldn't cut the PIR out to get down to the slab. You'd be putting a cold strip right at the door, which is already the weakest spot, and you risk nicking the DPM underneath. Just make sure the DPM is still intact in there before you fill

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.