I have spoken to a few local ASHP installers in Hampshire and the moment I mention to them about using the ASHP in cooling mode and having a split system which enables the UFH to be run above dew point in the summer, but have the upstairs fan coils with condensate drains to run at a colder temperature, they just tell me "No, you cannot do that".  Now, I am sure I have read on here, that people are doing just that.

If anyone is doing that, do you have a diagram or even a contact in the Wiltshire/Hampshire/Berkshire/Surrey area of a heating engineer who know and can do what I am trying to do. 

Posted

Here is a Haier scheme, you just setup as a 2 zone system. Each zone with a different flow temp fixed or WC. The image shows a buffer which is unlikely to be needed