Selfbuildsarah Posted 7 hours ago Posted 7 hours ago Someone has just raised something I haven’t come across so far - do we need antifreeze in our ufh?
JohnMo Posted 7 hours ago Posted 7 hours ago (edited) If you are in the build stage and it's likely to see near freezing temperatures and the loops are being left water filled, yes. If no water in system yet, just pressure test with air and leave pressurised. But you could blow out the water and replace with air pressure if already water filled. If house is built and heating system in use, no point. But you do need corrosion inhibitors and biocide (from same company to ensure chemistry compatibility) Edited 7 hours ago by JohnMo 1
Bancroft Posted 6 hours ago Posted 6 hours ago +1 for @JohnMo's comment. I too was a little confused about this so I spoke to a UFH supplier and they confirmed - it's just there for the commissioning/build period then flush out and replace with water (plus inhibitors/biocide if you feel the need). 1