Duncan62 Posted Tuesday at 22:03 Posted Tuesday at 22:03 Hello all, thanks to the fantastic BH I've had a go at my UFH / DHW install. Be nice (please!) but tell me if it's wrong! Q1: how do I go about filling the system? Do I use the full and flush valve, hose pipe? Or pipe in a hep2o from mains? Q2: I have a huge plastic container of glycol for anti freeze. How do I get that in the pipes? How do I get the correct ratio? Observations: DHW Will loop to UVC, but currently loops back to exit so I can get the system running as I need to commission the slab with heat cycle.
Nickfromwales Posted Tuesday at 22:36 Posted Tuesday at 22:36 31 minutes ago, Duncan62 said: Hello all, thanks to the fantastic BH I've had a go at my UFH / DHW install. Be nice (please!) but tell me if it's wrong! Q1: how do I go about filling the system? Do I use the full and flush valve, hose pipe? Or pipe in a hep2o from mains? Q2: I have a huge plastic container of glycol for anti freeze. How do I get that in the pipes? How do I get the correct ratio? Observations: DHW Will loop to UVC, but currently loops back to exit so I can get the system running as I need to commission the slab with heat cycle. Nice work. You need to tee into the hard cold mains feed and connect this part of the “filling loop”. Don’t use softened water. That filling loop is how you fill the heating system. Fill and test for leaks without treating it, check for the next 48/72 hrs to be certain you’re kosher, and only then do you put the glycol in. 1
JohnMo Posted Tuesday at 22:39 Posted Tuesday at 22:39 30 minutes ago, Duncan62 said: freeze. How do I get that in the pipes? How do I get the correct ratio Best ratio - is no glycol at all - why are you adding. It just degrades system performance. If you really want freeze protection for warranty, buy two anti freeze valves. But ones that respond to water temperatures not outside temperature. The flexible hose by the expansion vessel, should tee into the cold water main and act as filling loop. But you UFH loops will need filling and air got out of the system - you would use a hose on the UFH manifold for that, one loop at a time. Not seeing many useful auto bleed points
Nickfromwales Posted Tuesday at 22:39 Posted Tuesday at 22:39 These 2 are supposed to be the other way around, so you can clean / service / replace the double check valve by turning the stopcock off. Should be a quick swap with just a spanner. 1
Nickfromwales Posted Tuesday at 22:41 Posted Tuesday at 22:41 3 minutes ago, JohnMo said: Best ratio - is no glycol at all Not if the ASHP manufacturer states that it is mandatory, in the MI’s. Bottle vent on the manifold seems to be suffice, as it looks to be the highest point there. The feeds to upstairs should vent through the heating up there, vent on manifold #2 or rads.
JohnMo Posted Tuesday at 22:50 Posted Tuesday at 22:50 3 minutes ago, Nickfromwales said: Not if the ASHP manufacturer states that it is mandatory, in the MI’s. True, but do any modern ASHPs say glycol is the only option? 1
Nickfromwales Posted Tuesday at 22:53 Posted Tuesday at 22:53 Just now, JohnMo said: True, but do any modern ASHPs say glycol is the only option? Whether we like it, or dislike it, agree or disagree, the manufacturers installation guide is the bible. Some dont stipulate, some do, some are happy with anti-freeze valves, which I opted for on the last ones where I had 'free reign', but we should make the OP aware that they need to check if they are OK to deviate. Me personally, I hate the thought of glycol. No need for it, but there is always the power cut in the arse of winter to consider as worst-case.
Duncan62 Posted 17 hours ago Author Posted 17 hours ago 9 hours ago, JohnMo said: Not seeing many useful auto bleed points There is just 1 currently, as nick pointed out, on the UFH manifold. The pipes running upstairs are for a FCU and there is no bleed on them. Shall I add one up there?
Duncan62 Posted 17 hours ago Author Posted 17 hours ago 8 hours ago, Nickfromwales said: Me personally, I hate the thought of glycol. No need for it, but there is always the power cut in the arse of winter to consider as worst-case. Thanks guys. I shall check the manufacturers booklet again. Perhaps the actual flow temp anti freeze valve is best... I certainly don't want to compromise on CoP!
Duncan62 Posted 17 hours ago Author Posted 17 hours ago Q3: How much"flushing" of the system is required? I've put it together and been very careful along the way. Happy to flush, presume that's what the fill flush valve is for, so I can have the dirty water exit before the HP. Just want to know how critical this step is.
Nickfromwales Posted 17 hours ago Posted 17 hours ago 9 minutes ago, Duncan62 said: The pipes running upstairs are for a FCU and there is no bleed on them. Shall I add one up there? Double check that Of there’s definitely not one, then yes it’ll need an auto air vent. 7 minutes ago, Duncan62 said: Thanks guys. I shall check the manufacturers booklet again. Perhaps the actual flow temp anti freeze valve is best... I certainly don't want to compromise on CoP! Do as the good book says, because if you deviate you’ll be without warranty. Don’t ring their tech support to ask verbally, if you decide you’d like to explore this intensively, and ask them by email; if they say to use glycol in the book but say you can omit it, you’ll need that in writing. 4 minutes ago, Duncan62 said: Q3: How much"flushing" of the system is required? I've put it together and been very careful along the way. Happy to flush, presume that's what the fill flush valve is for, so I can have the dirty water exit before the HP. Just want to know how critical this step is. Do you have a particulate filter in the line? Usually a large 1/4 turn isolator with a big hex nut that you undo, with a small stainless steel gauze filter inside. 1
Duncan62 Posted 16 hours ago Author Posted 16 hours ago 23 minutes ago, Nickfromwales said: Do you have a particulate filter in the line? Usually a large 1/4 turn isolator with a big hex nut that you undo, with a small stainless steel gauze filter inside. I have the filter on the outflow, an Intaklean unit. Nothing anywhere else.
JohnMo Posted 16 hours ago Posted 16 hours ago 40 minutes ago, Duncan62 said: I have the filter on the outflow, an Intaklean unit. Nothing anywhere else. Again check your install instructions - mine explicitly stated a strainer must be installed and you’ve provided one. It also says if you have magnetic filter they also had to be installed
JohnMo Posted 16 hours ago Posted 16 hours ago 1 hour ago, Duncan62 said: How much"flushing" of the system is required? If it's all new nothing much, enough to get air out. Circulation pump on for an hour, cleaner filter and strainer
Nickfromwales Posted 16 hours ago Posted 16 hours ago 42 minutes ago, Duncan62 said: an Intaklean unit. Is it heat pump specific? You need a particle filter as well as a magnetic filter to catch all types of debris.
Duncan62 Posted 11 hours ago Author Posted 11 hours ago 4 hours ago, Nickfromwales said: Is it heat pump specific? You need a particle filter as well as a magnetic filter to catch all types of debris. Oh ok. Where in the loop do I need that, any recommendations for make?
JohnMo Posted 10 hours ago Posted 10 hours ago After the existing filter last thing in the return loop on its way to heat pump. Altecnic 1” Filter Ball Valve - 124-6005 CST or Inta Full Bore Ball Valve with Filter Cartridge - 28mm Comp. 1
Nickfromwales Posted 10 hours ago Posted 10 hours ago 1 hour ago, Duncan62 said: Oh ok. Where in the loop do I need that, any recommendations for make? Seems you’re off the hook mate 1
Duncan62 Posted 6 hours ago Author Posted 6 hours ago These anti freeze valves seems pricey: https://www.macdonaldplumbingsupplies.com/heat-pumps-accessories-c682/anti-freeze-valves-c685/inta-28mm-anti-freeze-valve-zero28-p16592 Over £100 per...
Duncan62 Posted 5 hours ago Author Posted 5 hours ago 10 minutes ago, JohnMo said: Look on eBay - half the price Do I need one on flow and return? Or just one, before the heat pump outside?
JohnMo Posted 4 hours ago Posted 4 hours ago One each side, so two, you then ensure the piping and heat exchanger within the heat pump are protected 1
Duncan62 Posted 4 hours ago Author Posted 4 hours ago Magic thanks.. ordered some freeze valves. Q4: Is it standard practice to put BOTH inhibitors and biocides in the UFH loop?
JohnMo Posted 3 hours ago Posted 3 hours ago Not standard, but best practice, especially if you are doing cooling as well. Make sure the two products are from same manufacturer. I use Adey MCP1+ and MC10+ rapide, can be sprayed into the filling loop, takes 30 seconds. Do once you have all the air out the system and no leaks.