Looking for a bit of Earthing advice

Got a small dedicated consumer unit (RCD/RCBO) whch is gounded by main supply & earth rod.
About a metre away is a metal garden lampost which is grounded via the CU supply.  

Mate thinks it needs it's own earth rod, but it has it's own earth rod via the nearby CU.
Not asking to win an argument, just want to know if the existing setup is compliant.   

Thanks
Ed  

 

Posted

What type of earth does the main property that is feeding this small CU have?

 

You say this CU has it's own earth rod, so are you saying it has a connection the the main house earth AND it's own earth rod connected?

 

Is the metal lamp post supported by being buried in the ground?

Posted (edited)
1 hour ago, ProDave said:

What type of earth does the main property that is feeding this small CU have?

 

You say this CU has it's own earth rod, so are you saying it has a connection the the main house earth AND it's own earth rod connected?

 

Is the metal lamp post supported by being buried in the ground?


Hi Dave,
House has an earth rod and yes the supply from the house connects to the satelite CU with it's own earth rod. 

Lampost is set in concrete about a metre deep. 

Ed

 

Edited by Ed21
Posted

That should all be fine then.  The issues can arise with PME / TNCS earthing by the supplier that has a known failure mode that can raise certain dangers if exported outside the house and that does not seem to apply here.