Trying to figure out why our heating loop is losing pressure, being dumped down tundish. 

 

One thing I noticed, is that the the systems shuts down/heat demand stops, the pressure jumps up per picture below.

 

Could this pressure jump, cause a pressure valve to trip, dumping down the tundish? 

20250925_185953.jpg

Posted

Jumping from about 0.75 bar (I usually keep it at 1.5bar) ,

 

A plumber came out and had a quick look, felt expansion vessels were OK, but that my pressure loss might be due to a pressure vessel being too small for the size of UFH loop (250sqm at 150 spacing, vessel is 18l)... But for me to check. I was also keeping the system at 1.5 bar, but he said drop it to 0.75 bar and see if that makes any difference. 

 

Nothing else jumped out at him got why I'm loosing pressure, but I didn't tell him about this pressure 'boost' which I just noticed.

 

 

Posted

I would suspect the EV pressurisation level, my installers left it at the factory setting of 3 bar, far too high. If it is too high or too low it will not be serving any useful purpose - and so appear to be too small.

 

You cannot check it while the system is working, you need first to release the pressure in the primary circuit completely when it is all cold.

 

Then adjust the pressure at the Schrader valve to be just below your chosen system pressure, say 1.2 bar, before re-pressurising the circuit to 1.5 bar or whatever.

 

This ensures the bladder will be slightly compressed by default but capable of accomodating 80% of its nameplate volume in expansion and/or pressure surges.

Posted

If it's a new system then it could be an undersized expansion vessel but if it's been in service for a while the much more likely the expansion vessel has lost its pressure or the diaphragm has failed.

  • Like 1
Posted

Thanks all, is there any risk to asking the plumber to fit a bigger expansion vessel anyway? For the sake of him coming out to check it, might Kurt replace It anyway? 

Posted
37 minutes ago, Andehh said:

Thanks all, is there any risk to asking the plumber to fit a bigger expansion vessel anyway? For the sake of him coming out to check it, might Kurt replace It anyway? 

Nope, you can never have too much expansion. If you’ve got the space on the wall just bang a bigger one in.

  • Thanks 1
Posted

No problem fitting a bigger expansion vessel, but if this EV is in an existing and previously working system, why do you and your plumber think its suddenly become to small??

  • Like 1
Posted
3 hours ago, Dillsue said:

No problem fitting a bigger expansion vessel, but if this EV is in an existing and previously working system, why do you and your plumber think its suddenly become to small??

 

Yes. And if he does not know how to check/adjust the pressure in the current one (see upthread) he won't know how to commission the new one so £150 down the drain and no improvement.

 

Going back to the original post I think there is perhaps a pressure spike when the system shuts down, that's quite likely depending on where the p.v. is in relation to the pump, but correctly set up it should absorb it without difficulty.

Posted (edited)

ASHP 12kw, with 230sqm of 16mm pipe, at 150mm spacing. 

 

Run temp is prob low 40s/high 30s? 

 

18L expansion vessel.

 

This pressure drop has been around since early on in the post installation phase. We had it for most of last winter, and maaay have had it during our first winter... We just had so many other bigger post move in focus points it wasn't a priority.

 

So it may have been there originally, it may have gotten worse year in year? 

Edited by Andehh