jack Posted August 15, 2025 Posted August 15, 2025 The overtemperature/pressure valve on my pressurised DHW tank has started leaking (again). This is the model: My understanding it that it's a combined temp/pressure release valve (there's a separate 3.5 bar overpressure valve connected to the same tundish). I also remember reading that these types of valves have a tendency to leak after they've been triggered, or even after testing. This is the second time this one has failed. Last time, the bladder on the expansion vessel had failed without me realising, leading to higher than usual system pressure. However, I don't now whether that was the cause of the valve failure. Our static pressure is less than 3 bar, so I doubt the system has ever seen anything like 4.5 bar, even with the immersion diverter working. I wonder whether the immersion diverter is occasionally causing the temperature near the top of the tank to exceed the trigger temp for this valve? I recently installed the relay module on our Eddi immersion diverter, which will let me control the maximum temperature better. I also have a couple of spare pockets that I could use for something like a solar mixing pump, but I'd rather avoid any more complexity. So my questions: If you had to speculate, what do you think is the most likely source of failure? If it's likely to be temperature, are there brands of valve that are better at coping with being triggered and returning to closed without leaking? What is the most appropriate pressure for my expansion vessel? Anything else I should be thinking about? Thanks as always.
Nickfromwales Posted August 15, 2025 Posted August 15, 2025 Give it a dozen cracks open, and slammed shut. See if that clears any debris which is what is usually the issue. Give that a whizz and report back. Immersion very likely the culprit, or not enough expansion volume. Do you have an HRC circuit on the DHW?
jack Posted August 15, 2025 Author Posted August 15, 2025 Thanks Nick. 56 minutes ago, Nickfromwales said: Give it a dozen cracks open, and slammed shut. See if that clears any debris which is what is usually the issue. I tried that a few times earlier, but could try it a few more times and see what happens. 56 minutes ago, Nickfromwales said: Immersion very likely the culprit, or not enough expansion volume. Do you have an HRC circuit on the DHW? No HRC circuit. I just checked and the expansion vessel had no pressure. Bah! So likely that, possibly made worse by the immersion diverter. I need to put a reminder in to check the pressure in the expansion vessel more regularly.
Nickfromwales Posted August 15, 2025 Posted August 15, 2025 3 minutes ago, jack said: Thanks Nick. I tried that a few times earlier, but could try it a few more times and see what happens. No HRC circuit. I just checked and the expansion vessel had no pressure. Bah! So likely that, possibly made worse by the immersion diverter. I need to put a reminder in to check the pressure in the expansion vessel more regularly. I’d double the amount of volume, by adding to it with a second vessel plumbed in in parallel. That’ll give you ample headroom for immersion higher temp top ups, as tbh you don’t want to lose out on those really. TBH x2, I’d just install 2 new matching units and draw a line under it, in case the existing has become fractured.
jack Posted August 15, 2025 Author Posted August 15, 2025 59 minutes ago, Nickfromwales said: Give it a dozen cracks open, and slammed shut. See if that clears any debris which is what is usually the issue. Give that a whizz and report back. Did it ~15 times aggressively but no luck. Any recommendations for an alternative brand? 38 minutes ago, Nickfromwales said: One big one obvs if you have space. What's "big" in this context? It's a 22 L tank for a 250 L unvented cylinder. Minimum appears to be something like 4-5%, but rule of thumb is 10%, so it's above the minimum but a little short of the rule of thumb. The bladder on the original one died a few years ago, so I replaced it with a new one with a replaceable bladder. I'd ideally rather hang onto that than replace it again, although if it's important, I'm pretty sure I have the space for a larger one. Any brand you'd recommend?
Nickfromwales Posted August 15, 2025 Posted August 15, 2025 Zimlet are popular, and tbh most mainstream names prob just stick their mark on these anyways. Once you sort the expansion, I’d say just double it, you’ll be able to fit the same T&PRV (Reliance is industry standard) and the issue will go away. 1
jack Posted August 15, 2025 Author Posted August 15, 2025 1 hour ago, Nickfromwales said: What’s the immersion set temp? I'd need to check, but definitely nothing like 90 deg. The issue is that the immersion is quite low on the tank (the upper immersion died and I've never gotten around to replacing it). By the time that lower region of the tank gets hot enough to turn off the immersion, there's been a lot of time for the water at the top of the tank to get very hot due to convection. That was my thinking when I mentioned a destratification pump. 1
jack Posted August 16, 2025 Author Posted August 16, 2025 21 hours ago, Nickfromwales said: Give it a dozen cracks open, and slammed shut. See if that clears any debris which is what is usually the issue. Right, I've had a bit of time this morning to look more closely at this. It's actually the pressure relief valve that's failed. The 15 mm pipework from outlets of the PRV and the PTRV joins before the tundish (I assume that's acceptable?), so it isn't possible to tell which one's failed without disconnecting the pipework from the valve outlets. The failed valve is a Reliance 102-series 3.5 bar PRV. Apparently that's a "cold water only" valve. I think this was the valve originally supplied with the cylinder, but it's also possible I asked that it be replaced at the same time I had the TPRV replaced a few years back. Either way, it doesn't appear to be the correct valve for this application. Annoyingly, none of the Reliance valves designed for hot water systems come in a 3.5 bar variant. There's 107 series that is allegedly for "cold water use only", but it has a 110° max working temp. Shame I didn't realise what was going on yesterday or I could have given their technical department a call to see what the deal is there. On the assumption that I shouldn't increase to a 4 bar version, and a 3 bar version is too low given I'm already having issues with the 3.5 bar version, I may need to look elsewhere. Annoyingly, I can't see any obvious options with the same form factor, inlet fitting, and outlet fitting. If the Reliance 107 model mentioned above isn't suitable, it might be time to replace both valves with a different brand and adapt the outlet pipework to suit. Anyone have any thoughts?
Nickfromwales Posted August 16, 2025 Posted August 16, 2025 24 minutes ago, jack said: Right, I've had a bit of time this morning to look more closely at this. It's actually the pressure relief valve that's failed. The 15 mm pipework from outlets of the PRV and the PTRV joins before the tundish (I assume that's acceptable?), so it isn't possible to tell which one's failed without disconnecting the pipework from the valve outlets. The failed valve is a Reliance 102-series 3.5 bar PRV. Apparently that's a "cold water only" valve. I think this was the valve originally supplied with the cylinder, but it's also possible I asked that it be replaced at the same time I had the TPRV replaced a few years back. Either way, it doesn't appear to be the correct valve for this application. Annoyingly, none of the Reliance valves designed for hot water systems come in a 3.5 bar variant. There's 107 series that is allegedly for "cold water use only", but it has a 110° max working temp. Shame I didn't realise what was going on yesterday or I could have given their technical department a call to see what the deal is there. On the assumption that I shouldn't increase to a 4 bar version, and a 3 bar version is too low given I'm already having issues with the 3.5 bar version, I may need to look elsewhere. Annoyingly, I can't see any obvious options with the same form factor, inlet fitting, and outlet fitting. If the Reliance 107 model mentioned above isn't suitable, it might be time to replace both valves with a different brand and adapt the outlet pipework to suit. Anyone have any thoughts? Ok. Exactly where is this valve. Is it the cold mains ‘blow off’ on the control group block? If so, it should be minimum 5 bar or even 6 bar, as factory.
jack Posted August 16, 2025 Author Posted August 16, 2025 It's on the cylinder. To save me going and taking a photo, this is how it came from the manufacturer (McDonald Cylinders): The one on the left is the PRV, which is what's failed. Interestingly, this diagram shows a light blue handle on the valve, which accords with the 107-series ("cold only", but rated to 110° C) Reliance valve I mentioned above.
Nickfromwales Posted August 16, 2025 Posted August 16, 2025 41 minutes ago, jack said: It's on the cylinder. To save me going and taking a photo, this is how it came from the manufacturer (McDonald Cylinders): The one on the left is the PRV, which is what's failed. Interestingly, this diagram shows a light blue handle on the valve, which accords with the 107-series ("cold only", but rated to 110° C) Reliance valve I mentioned above. I’ve NEVER ever seen one of those fitted, that’s bloody rubbish. You can’t have a PRV that’s the same or lesser than the one on the CG!! That needs deleting imho.
Nickfromwales Posted August 16, 2025 Posted August 16, 2025 Have you got a pic of their CG as installed plz?
jack Posted August 16, 2025 Author Posted August 16, 2025 14 minutes ago, Nickfromwales said: Have you got a pic of their CG as installed plz? There's no control group as such. There's a pressure reducing valve on the incoming main. It's a bit hard to get to and I can't remember the pressure it's set at, but possibly 3 bar? Our static water pressure is typically around 2.8-3 bar I think. There's no pressure relief valve at that point. I'd be happy to use this opportunity to rejig the whole setup tbh. The dynamic water pressure's always been a bit shite, probably at least partly due to the pressure drop across the water softener. There's been the odd weep from a couple of the connections that I want to sort out too.
jack Posted August 16, 2025 Author Posted August 16, 2025 17 minutes ago, Nickfromwales said: I’ve NEVER ever seen one of those fitted, that’s bloody rubbish. You can’t have a PRV that’s the same or lesser than the one on the CG!! That needs deleting imho. Incidentally, this is the same setup as Altecnic (possibly rebadged? I know McDonald and another manufacturer sell exactly the same cylinder we bought from them):
Nickfromwales Posted August 16, 2025 Posted August 16, 2025 @jack From that link I think you had a monkey boy change that and he’s installed the wrong one. Just makes zero sense whatsoever. Stinks of (2nd) installer error.
jack Posted August 16, 2025 Author Posted August 16, 2025 Nope. Cylinder manufacturer's instructions say this is supplied with a 3.5 bar PRV: (The guy was a complete monkey though. Installed the water softener isolation valves the wrong way around, so you wouldn't have been able to isolate the unit. I sorted it was wrong the second a looked at it. He failed to screw the waste trap onto its fitting when he was done, which I only learned about several months later when I found mould growing behind the tank. And the pipework he assembled for the water softener was crooked and put a lot of sidewards force onto some of the fittings. And my wife wonders why I don't just get trades in to do things that need doing around the house!)
Nickfromwales Posted August 16, 2025 Posted August 16, 2025 That 3.5bar relief is just stupid. The PRedV sorts you out at 3.0 or 3.5bar incoming, and protection against that failing is a 5/6 or even 8 bar PRV, usually on the inlet control group. What a shit design! Sorry.
jack Posted August 16, 2025 Author Posted August 16, 2025 2 hours ago, Nickfromwales said: That 3.5bar relief is just stupid. The PRedV sorts you out at 3.0 or 3.5bar incoming, and protection against that failing is a 5/6 or even 8 bar PRV, usually on the inlet control group. What a shit design! Sorry. Ha, no need to apologise, I'd rather have the honest feedback. I assume the reason for the low relief valve pressure is that this is a copper cylinder, which I expect has a lower max pressure than stainless steel?
Nickfromwales Posted August 16, 2025 Posted August 16, 2025 24 minutes ago, jack said: Ha, no need to apologise, I'd rather have the honest feedback. I assume the reason for the low relief valve pressure is that this is a copper cylinder, which I expect has a lower max pressure than stainless steel? Yup. I think the increase in expansion volume may aid this situation, and hopefully keep the cylinder static pressure in check; in an ideal design it should be away from the threshold it is living at, eg its obvious that this lives at/on the absolute limit of what the valve is set to react at. The fact it was copper is probably in amongst the trail here, I just assumed stainless, sorry again lol. Adding some more expansion volume is what I would do, if I was asked to sort this out away from here, so that’s what I’d advise you to do. Should put it to bed once and for all. 1
John Carroll Posted August 17, 2025 Posted August 17, 2025 (If) You wish to retain a 22L EV with the pressure reducing valve (PRV) set to 2.5bar, at this setting and with a EV precharge setting of 2.3bar (ideally) then after a full reheat to 60C the final pressure will be 3.35bar, and if reheated to 65C will be 3.49bar, both too close IMO to the expansion valve setting of 3.5bar. If you reduce the PRV to 2.0bar and the EV precharge pressure to 1.8bar then the final pressures become 2.74bar at 60C & 2.86bar at 65C. If you install a 35L EV then with the PRV set to 2.5bar and EV precharge at 2.3bar will result in a final pressure of 2.99bar at 60C & 3.06bar at 65C, (and still OK at 3.19bar at 70C). If you require a UV cylinder pressure at the "normal" 3.0bar then you will require a EV vol of 65L with the PRV set to 3.0bar and a EV precharge of 2.8bar to give comfortable final pressures of 3.28bar at 60C and 3.32bar at 65C.
jack Posted August 18, 2025 Author Posted August 18, 2025 19 hours ago, John Carroll said: (If) You wish to retain a 22L EV with the pressure reducing valve (PRV) set to 2.5bar, at this setting and with a EV precharge setting of 2.3bar (ideally) then after a full reheat to 60C the final pressure will be 3.35bar, and if reheated to 65C will be 3.49bar, both too close IMO to the expansion valve setting of 3.5bar. If you reduce the PRV to 2.0bar and the EV precharge pressure to 1.8bar then the final pressures become 2.74bar at 60C & 2.86bar at 65C. If you install a 35L EV then with the PRV set to 2.5bar and EV precharge at 2.3bar will result in a final pressure of 2.99bar at 60C & 3.06bar at 65C, (and still OK at 3.19bar at 70C). If you require a UV cylinder pressure at the "normal" 3.0bar then you will require a EV vol of 65L with the PRV set to 3.0bar and a EV precharge of 2.8bar to give comfortable final pressures of 3.28bar at 60C and 3.32bar at 65C. Thanks John, it sounds like a larger (or additional) expansion vessel is definitely needed, as per @Nickfromwales's suggestion.
John Carroll Posted August 18, 2025 Posted August 18, 2025 (edited) 1 hour ago, jack said: Thanks John, it sounds like a larger (or additional) expansion vessel is definitely needed, as per @Nickfromwales's suggestion. You said the EV was flat, what pressure was it recharged to?, it should also have been done at the very least with the cold mains to the cylinder shut off and a HW tap opened, if its located above the cylinder then that should be OK. I would also suggest checking that there is a pressure reducing valve (PRV) installed (which there should be) on the cold water valve set and most/more important that its setting is checked. Even with your 22L EV and assuming that you will rarely if ever be reheating a full cylinder, more likely say 80% or 200L then a final pressure of 3.12bar at 60C & 3.25bar at 65C with a cyl prepressure of 2.3bar, 2.5bar (if available) will still give over 90% flowrate of a 3.0bar cylinder. Is the blue PRV next to the (red) TPR also stamped as set to 4.5bar? Edited August 18, 2025 by John Carroll