Sunil237 Posted December 7, 2024 Posted December 7, 2024 (edited) Hi all, I saw some really nice ideas on using manifolds from the cold feed and from the dhw to distribute through the house. I have a few specific questions related to my plan I hope you all can help guide me on. My project is a full house refurb and extension. I'll have 3 bathrooms, 1 kitchen, 1 washing machine connection (at the back of a bathroom), and hot and cold to taps outside. My current thought is to do this; Hep20 fittings and pipes New 25mm MDPE to plant room > 22mm stop cock > water meter > 4x (each bathroom & to cylinders) 22mm manifold ports + 2x (kitchen & outside) 15mm manifold ports > at each location secondary manifold to feed each appliance/fitting with 15mm The above would then be repeated to supply hot water but 1 less 22mm manifold ports as I can exclude the cylinder. Questions; 1) is it ok to go from a manifold to another? 2) should I use 15 or 22mm to go from the manifold to the secondary manifold? 3) Should I use 10 or 15mm to go from secondary manifold to appliance/fitting? 4) Is there a better brand to use for this type of system? I am using hep20. 4) does the order of the manifold matter? 5) any other tips? 6) is the general layout of my idea ok? Any suggestions? I really hope I haven't misunderstood all this manifold stuff! Thanks in advance Edited December 7, 2024 by Sunil237
JohnMo Posted December 7, 2024 Posted December 7, 2024 A sketch of your proposal would make it clearer what you propose. An idea of distance also would be good.
Nickfromwales Posted December 7, 2024 Posted December 7, 2024 It’s pointless going manifold to manifold, as that defeats the whole object imo. Having higher volumes of ‘dead legs’, before basin taps in particular, means that you’ll waste a lot of water/energy getting premium temp (hot) water out of high-frequency/low volume outlets (if there’s no hot return circuit). Not a concern for baths and shower, less of a concern for kitchen/utility taps, but defo a sticking point with basins where you just want to flick the tap on and wash your hands. Stick with Hepworth, it’s all I use these days and is simply bombproof. Where failures occur is when someone installs the pipework and scratches the outside diameter linearly causing leaks/weeping joints. If there’s a few turns and twists the simply install offcuts of 25mm flexible conduit at these points and draw the pipe through them; particularly helpful if doing this on your own (single handed). These can stay in to allow some movement if necessary, and this should be considered for longer hot runs where the pipe will expand/contract a little with temp changes. Without distances from the cylinder to the outlets, and what they do, it’s impossible to advise on pipe size On 07/12/2024 at 16:17, JohnMo said: A sketch of your proposal would make it clearer what you propose. An idea of distance also would be good. Expand what he said
Sunil237 Posted December 11, 2024 Author Posted December 11, 2024 Sorry for the delayed response, ill kids thanks @JohnMo & @Nickfromwales Here are some sketches. I do not have a proper floor plan for first floor unfortunately. I plan to feed my new cold water main (green square) into the plant room which is located at the centre of the ground floor, my house will be 10m wide x 11m deep on ground floor, and 10m wide x 6m deep on 1st floor. There is no plan to put in a hot circuit. The plant room will also house my hot water cylinder, the purple square. The approx run lengths, including verticals, to these rooms are as follows; Kitchen: 12m Kitchen sink, dishwasher, fridge, outdoor taps (h&c) Outside rear wall: 12m outdoor taps (h&c), shower, future hottub. Downstairs WC: 8m Basin tap, toilet, future shower Utility room: 8m Washing machine directly behind WC. Family bathroom: 8m Basin tap, toilet, bath, shower En-suite: 8m Basin tap, toilet, shower Happy to consider individual pipes if a secondary manifold method is the wrong way to go. But it then takes me to 28 feeds + 1 for cylinder all within the plant room and approx 300m of pipe.
JohnMo Posted December 11, 2024 Posted December 11, 2024 I would just keep it simple One hot and one cold manifold in plant room. Then one of the two options below. Option 1. Looks like a 5 port manifold for hot and cold. A single 15mm feed from manifold to each wet room, in hot and cold. From 15mm pipe in wet rooms, teeing off to users - sink, toilet, shower etc. (this what I did and have seen no issues. 2. Bigger manifold in plant room, with individual (suitable sized pipes) to each user in the house. So a mix of 10 and 15mm. 2
torre Posted December 11, 2024 Posted December 11, 2024 We did the same as @JohnMo 's option 1. All run in 15mm Hep2o so no joints at all from a manifold (with isolation) all the way to each room (so each room is easily isolated and can be worked on separately). There you can just tee off as needed or use a secondary manifold (with or without isolation) if that works better (Hep2o manifolds are just a block of tees at the end of the day). For some rooms we reduced down to 10mm for basins just to make the runs easier to work with.
Sunil237 Posted December 11, 2024 Author Posted December 11, 2024 Thanks John and torre For option 1, is there any con in using 22mm from the manifold to the wet rooms? I have a decent length of hep 22mm piping that I would like to use up For option 2, if I'm able to this I could only do it with plastic manifold fittings due to the cost. Any disadvantages compared to the brass manifold? Any suggestions on manifolds? I only see a few options here but a few different systems in US Thanks
Nickfromwales Posted December 11, 2024 Posted December 11, 2024 On 11/12/2024 at 14:16, Sunil237 said: Thanks John and torre For option 1, is there any con in using 22mm from the manifold to the wet rooms? I have a decent length of hep 22mm piping that I would like to use up For option 2, if I'm able to this I could only do it with plastic manifold fittings due to the cost. Any disadvantages compared to the brass manifold? Any suggestions on manifolds? I only see a few options here but a few different systems in US Thanks Expand Use the 22mm up on the cold runs first, hot runs last, but preferably use 15mm for the hot feeds wherever possible (10mm where it's a basin and close (less than 10m) to the cylinder). Decide if you want / need to be able to isolate every single run, and if not you can go with the plastic dumb manifolds to save a lot of £'s. 1
Sunil237 Posted December 26, 2024 Author Posted December 26, 2024 Thanks for the feedback. I'm thinking of using mlcp instead of hep2o. I've found a nice manifold system with riifo https://www.bes.co.uk/riifo-plumbing-manifold-3-4-x-1-2-valved-outlets-4-port-blue-levers-27473/ But wondered if I need to stick with riifo pipe and fittings, or if everything is interchangeable? Is there a brand that's preferred and that would be around for years to come? Thanks
Nickfromwales Posted December 27, 2024 Posted December 27, 2024 On 26/12/2024 at 13:34, Sunil237 said: Is there a brand that's preferred and that would be around for years to come? Expand Yes, Hepworth, lol. Those BES manifolds are good value for money, and from the pics they may be cone faced 1/2” males so may take a standard nut and olive and allow a direct connection with copper. Failing that and them being true 1/2” male threads, then the Hep2o fittings could be used to convert “iron to copper” LINK and you’re off to the races. Add the costs of the extra time / fittings, though, and you’re not much better off tbh. MLCP tends to be less forgiving IMO, for long runs and 1st fixing, so I prefer the user-friendly flexibility of standard Hep2o pipe. Everything will be interchangeable, but if you use a particular pipe you should use their fittings; eg I won’t use John Guest fittings on a Hep2o pipe installation (largely through fear of failure / warranty issues, as I install these things for 3rd party clientele vs myself so any doubt / risk must be managed or eliminated). 1
Sunil237 Posted January 5 Author Posted January 5 thanks for the help Nick, I'll be going with your recommendation and using Hep2o throughout. I'll be using the first manifolds I shared which are Hep2o and then just branching off once in each room with smaller diameter pipes. I figured that the secondary manifolds were probably going to cause more pain than help once the plumber gets into the actually practical fitting!
Nickfromwales Posted January 6 Posted January 6 On 05/01/2025 at 23:00, Sunil237 said: thanks for the help Nick, I'll be going with your recommendation and using Hep2o throughout. I'll be using the first manifolds I shared which are Hep2o and then just branching off once in each room with smaller diameter pipes. I figured that the secondary manifolds were probably going to cause more pain than help once the plumber gets into the actually practical fitting! Expand Some pics of my current project for example 👍 1
Sunil237 Posted February 22 Author Posted February 22 Thank you @Nickfromwales @torre and @JohnMo We've completed first fix and I'm super pleased with my water set up ☺️ As I have a joist in the room I can actually box off the pipework, keeping it fairly neat. I used hep2o manifolds with built in isolation, and regular branching at each room. The plumber wasn't so convinced that the manifold system will help any but did like that we could isolate the outdoor taps in winter. I used 22mm and 15mm hep 90 degree bends which the plumber found more useful than he thought they would be. The manifold bracket looks to have worked great! I see others used Munson clips but I bought the manifold mount just to try. I realise I've gone against advise here and have 22mm for the hot! Things just got done and I didn't catch on until a bit too late My components 15mm manifold (2 port, available in 2,3 &4) 22mm manifold (single port) Manifold mount 15 & 22mm 90 degree bends 3/4 iron to 22m compression 90degree manifold cap My plumber changed the end fittings over 2
Nickfromwales Posted February 23 Posted February 23 Looks good! The pipe bends (formers) do help get the pipe to go nicely into the fittings after a change in direction. Every day is a school day, as I didn’t know they made those brackets did the last one ‘stood off’ with Munson rings / bases / and threaded bar. Thanks for that, I’ll defo look into those from now on, just frustrating that every merchant I’ve purchased from for the last 10+ years have never had these displayed for sale or in the “people who bought this also bought…….” section.
Sunil237 Posted February 24 Author Posted February 24 On 23/02/2025 at 10:15, Nickfromwales said: Looks good! The pipe bends (formers) do help get the pipe to go nicely into the fittings after a change in direction. Every day is a school day, as I didn’t know they made those brackets did the last one ‘stood off’ with Munson rings / bases / and threaded bar. Thanks for that, I’ll defo look into those from now on, just frustrating that every merchant I’ve purchased from for the last 10+ years have never had these displayed for sale or in the “people who bought this also bought…….” section. Expand Glad to return some help 😅 My plumber said the bracket fit nicely on the 15mm manifold, but he had to use longer screws for the bracket holding on the 22mm manifold as it wasn't designed for that size 1