UFH Mixer Valve Query


calama

Recommended Posts

Hi I am wondering if the mixer valve would normally affect the flow rate? If I set the temperature to anything above 45deg then the flow meters barely register. But if I set it to minimum then I get 2lt/min at the flow meters. I can't get the correct temperature at the right flow rate to get a large room heated up. 

I would expect the mixer would just mix the hot input and cold return without affecting the flow...am I wrong or is it defective?

Thanks for any advice.

20241116_110359.jpg

Link to comment
Share on other sites

The mixing valves do die off with old age. Just put a new one in and you’ll be in the pub for Friday :)  15 years is a decent stretch for a part that’s constantly moving / adjusting etc.

Do you have a magnetic filter in the system? If not, I’d add one when you change the valve. 

Link to comment
Share on other sites

Ok thanks, yes I think that will have to be the plan. The system does have a mag filter on it and I flushed out the manifold separately...there was quite a bit just sitting in the bottom on the manifold so likely there is something in valve too.

Link to comment
Share on other sites