I am hoping someone can help as no plumber has been yet.

We have a Samsung 12KW ASHP (no issues with it)

We have UFH downstairs (no issues)

We have radiators upstairs.  When the radiators come on they cause significant noise and I cannot sleep.

We have had people look at it, balancing, draining etc.  Still the noise.  We have 7 radiators upstairs.  The noise is worst in the master bedroom and I think this is the first radiator.  It is hardly anything in the further bedrooms.  

The pipework is all the correct size.  I know very little but it sounds like it must be the water pressure / amount of water trying to get through?

Many thanks.

Link to comment
Share on other sites

10 hours ago, sirpatchuk said:

I am hoping someone can help as no plumber has been yet.

We have a Samsung 12KW ASHP (no issues with it)

We have UFH downstairs (no issues)

We have radiators upstairs.  When the radiators come on they cause significant noise and I cannot sleep.

We have had people look at it, balancing, draining etc.  Still the noise.  We have 7 radiators upstairs.  The noise is worst in the master bedroom and I think this is the first radiator.  It is hardly anything in the further bedrooms.  

The pipework is all the correct size.  I know very little but it sounds like it must be the water pressure / amount of water trying to get through?

Many thanks.

 

Have you smart radiator valves controlled by Evohome or such?

Check circ pump settings and post its make/model/mode/settings and flowrate if it displays it.

Check UFH manifold meter settings (throttled etc) and flowrates.

Does one circ pump serve the rads and the UFH?

Where is the expansion vessel located?.

Edited by John Carroll
Link to comment
Share on other sites

I have a few radiators that make some noise.  I think the fundamental problem is that you are trying to achieve a 5 C temperature drop across each radiator and this requires a much higher water flow rate than the 20 C drop that is typically used with boilers. This high flow rate can lead to noise.  You might be able to throttle the radiator valve to reduce the flow rate and so reduce or eliminate the noise but this will reduce the radiator output so you may or may not be able to do this and keep the room warm enough.