Garald Posted September 13, 2022 Author Posted September 13, 2022 On 13/09/2022 at 20:02, ReedRichards said: That's 2561 Watts at delta T = 50 C and, as you correctly observe, 0.41 times this, 1050 Watts for delta T = 25 C (sorry about the error in my earlier comment). Expand So, what power do I need to heat a 3.75x9.75m library to 20-21C when it's -7 C outside? (Assume it is well insulated: R of insulation at least 3.8, closer to 4.5 counting the brick wall and an air layer; I'm changing the double glazing, whose thermal perfornace is already high, by better double-glazing.) About 3 kW perhaps, so three of these radiators? Maybe put a fourth radiator in the broad corridor leading to it, since it will also be part of the library? (Put a cushy bench in front of that fourth radiator, especially for those who like to get toasted while reading?) (Anything significantly below -7C in Paris is basically Eurostar-stopping weather. If shove comes to push, well, you can see a working fireplace in the pictures.)
Garald Posted September 14, 2022 Author Posted September 14, 2022 Also, I guess this means I can take an old radiator that is now insufficient for the library or the main bathroom, say, and put it in a smaller space that needs to be heated (such as a WC), if there is room for it?
ReedRichards Posted September 14, 2022 Posted September 14, 2022 On 13/09/2022 at 23:02, Garald said: So, what power do I need to heat a 3.75x9.75m library to 20-21C when it's -7 C outside? Expand I am fortunate in that my installer did all the heat loss calculations for me (using some software called Heat Engineer). The biggest "room" in my house has a floor area of 48 m2 and was calculated to require about 2.8 kW of heat when it was -4 C outside. On 14/09/2022 at 05:54, Garald said: Also, I guess this means I can take an old radiator that is now insufficient for the library or the main bathroom, say, and put it in a smaller space that needs to be heated (such as a WC), if there is room for it? Expand Yes indeed; just make sure your installer flushes all the gunk out of it before it is relocated.
JohnMo Posted September 14, 2022 Posted September 14, 2022 On 13/09/2022 at 23:02, Garald said: So, what power do I need to heat a 3.75x9.75m library to 20-21C when it's -7 C outside? (Assume it is well insulated: R of insulation at least 3.8, closer to 4.5 counting the brick wall and an air layer; I'm changing the double glazing, whose thermal perfornace is already high, by better double-glazing.) Expand You have the spreadsheet, so easy enough to calculate. U value is 1/R, so R of 4.5 is 0.22 U value. Double glazed window U value 1.4, single glazed U value 5.
SteamyTea Posted September 14, 2022 Posted September 14, 2022 On 14/09/2022 at 08:12, JohnMo said: Double glazed window U value 1.4, single glazed U value 5. Expand Never thought to compare windows. It is a huge difference, wonder what my secondary glazed, double glazed windows U-Value is. And the secondary glazing is airtight (ish).
Garald Posted September 14, 2022 Author Posted September 14, 2022 On 14/09/2022 at 08:12, JohnMo said: You have the spreadsheet, so easy enough to calculate. Expand Do you mean the heat loss calculator? That seems designed for a house, not a room, and doesn't let me input U values.
JohnMo Posted September 14, 2022 Posted September 14, 2022 It does LL the white cells. Just size to suit room. Assume internal walls have no heat loss, as they are heated on the other side.
Garald Posted September 14, 2022 Author Posted September 14, 2022 (edited) On 14/09/2022 at 10:49, JohnMo said: It does LL the white cells. Just size to suit room. Assume internal walls have no heat loss, as they are heated on the other side. Expand LL? The (part-wooden) ceiling is below my (heated) attic, and the floor is mostly above a GP's (but his hours are short and he seems to be often on vacation), except for the part above my bikeshed (unheated, but will insulate the ceiling). 0 roof, 50% floor? Edited September 14, 2022 by Garald
JohnMo Posted September 14, 2022 Posted September 14, 2022 So LL, meant to type 'all' Ceiling, just use 0.1m2 for area to keep the calculation from throwing a miss calculation. Floor just assume it settles to 8 degrees the same as the ground above the shop. Then make an alteration to compensate for the area of the bike shed, which will cool to your lowest temperature.
Garald Posted September 14, 2022 Author Posted September 14, 2022 But I don't see any white cells for U or R.
Garald Posted September 14, 2022 Author Posted September 14, 2022 And I should use 0 doors, simce there is only 1 door, leading to a corridor thst will probably be heated? What U value for the floor?
JohnMo Posted September 14, 2022 Posted September 14, 2022 I would use no doors, just use the area of the external walls and windows. Floor u value? What's your insulation, have a play with something like this, others available. https://www.recticelinsulation.com/en-gb/u-value-calculator
Garald Posted September 14, 2022 Author Posted September 14, 2022 OK, here's the outcome. So, what's the verdict? Surely not 868W? That's way too low. Heat loss calculator - Master (1).xlsFetching info...
JohnMo Posted September 14, 2022 Posted September 14, 2022 (edited) I altered your wall U value, to 0.22 and it puts the heat loss at -10 degC at 1096W. Which sounds about right. Some perspective, my house 192m2 single storey, whole house heat loss is 3088W Edited September 14, 2022 by JohnMo Clarity
Garald Posted September 14, 2022 Author Posted September 14, 2022 That's really not very much. That's one very tall radiator (a bit over 1000W at low temperature). Maybe I should put two radiators like that, on opposite sides of the long inside wall. Does that make sense?
JohnMo Posted September 14, 2022 Posted September 14, 2022 The more surface area you have of radiators the lower the temperature needs to be to get the same heat output. Also water volume is good for heat pumps. Other question is do you need to size the system for -10 degrees?
Garald Posted September 14, 2022 Author Posted September 14, 2022 On 14/09/2022 at 15:34, JohnMo said: The more surface area you have of radiators the lower the temperature needs to be to get the same heat output. Also water volume is good for heat pumps. Other question is do you need to size the system for -10 degrees? Expand It's prudent to size it to -7 degrees (in that it's still fairly common, in that (I think) it happens most or nearly all years; no bougainvillias in Paris, though that may be changing). Anything less than -10 degrees is Eurostar-stopping, highway-closing. airport-disaster-movie weather. I certainly don't think I need to size the system for *less* than -10 degrees. If that ever happens again (not certain because of global warming), I can just use the chimney.
Garald Posted September 14, 2022 Author Posted September 14, 2022 On 14/09/2022 at 15:34, JohnMo said: Also water volume is good for heat pumps. Expand Wait, is this an argument for or against overcalculating?
JohnMo Posted September 14, 2022 Posted September 14, 2022 It's an argument for a large system volume and low flow temps. Over calculation of heat demand is not good, as system has less room to modulate to lower setting.
Garald Posted September 14, 2022 Author Posted September 14, 2022 OK. But what is the margin of error here? Perhaps I should aim at a maximum of 1500W, to be safe?
Garald Posted September 14, 2022 Author Posted September 14, 2022 (What scientists and math people say of engineers is that they do rather precise computations, with the necessarily imperfect data and models that they have, and then multiply everything by 2. I don't know whether this is an idealization or a slur.)
JohnMo Posted September 14, 2022 Posted September 14, 2022 On 14/09/2022 at 15:46, Garald said: OK. But what is the margin of error here? Perhaps I should aim at a maximum of 1500W, to be safe? Expand Why? That's a 50% or more oversize for the coldest day. They are are rare, a few days a year.
Garald Posted September 14, 2022 Author Posted September 14, 2022 I've kept U=0.22 and reduced the wall space to 36.56 (since two of the walls are internal). I get 847W, which is really low. Even if I set the wall space to 48.30 (because a short wall adjoins the kitchen, which won't be insulated - doing so would require ripping it apart) I get a total heat loss of 916W.
Recommended Posts