revelation Posted November 28, 2021 Share Posted November 28, 2021 Hi all We have underfloor heating fitted between joists on our FF and Loft. We have laid 18mm Caber boards over this, and before putting on the engineered wood flooring we were looking for the best underlay to use in this situation to help with heat transfer. Link to comment Share on other sites More sharing options...
SteamyTea Posted November 29, 2021 Share Posted November 29, 2021 (edited) This is an interesting problem as usually we are looking to thermally isolate elements, not join them together. Underlay also needs to deaden sound and allow some 'bounce' underfoot. So I thought I would look at two common materials, rubber and cellular rubber. These have thermal conductivities of 0.13 and 0.045 W.m-1.K-1 respectively. Now assuming that the underlay is only 6 mm thick, then: Rubber 0.006 [m] / 0.13 [ W.m-1.K-1] = 0.0462 [R = m2.K.W-1] 1 / 0.0462 [R] = 21.65 [U = W.m-2.K-1] Cellular rubber 0.006 [m] / 0.045 [ W.m-1.K-1] = 0.133 [R = m2.K.W-1] 1 / 0.133 [R] = 7.52 [U = W.m-2.K-1] So cellular rubber will be 3 times more insulating. Edited November 29, 2021 by SteamyTea Link to comment Share on other sites More sharing options...
Olf Posted November 29, 2021 Share Posted November 29, 2021 0.13/0.045 = 2.88 - yep, one is 3 times more insulating Not sure how flat the floor finish is, my understanding has always been that the purpose of the underlay is supposed to mask all the imperfections of the subfloor first and then add impact sound insulation. The product I'm looking at is https://www.interfloor.com/app/uploads/2016/08/Heatflow-Wood-Laminate-DURALAY-TS-3.pdf . Although R = 0.035 m² K/W, at 3mm thickness only it gives overall U=28.6 W/m²K. 3mm thickness requires decent floor finish though. Link to comment Share on other sites More sharing options...
revelation Posted November 29, 2021 Author Share Posted November 29, 2021 11 hours ago, SteamyTea said: This is an interesting problem as usually we are looking to thermally isolate elements, not join them together. Underlay also needs to deaden sound and allow some 'bounce' underfoot. So I thought I would look at two common materials, rubber and cellular rubber. These have thermal conductivities of 0.13 and 0.045 W.m-1.K-1 respectively. Now assuming that the underlay is only 6 mm thick, then: Rubber 0.006 [m] / 0.13 [ W.m-1.K-1] = 0.0462 [R = m2.K.W-1] 1 / 0.0462 [R] = 21.65 [U = W.m-2.K-1] Cellular rubber 0.006 [m] / 0.045 [ W.m-1.K-1] = 0.133 [R = m2.K.W-1] 1 / 0.133 [R] = 7.52 [U = W.m-2.K-1] So cellular rubber will be 3 times more insulating. I appreciate the detail. Our floors are reasonably flat as we had new joists out in and the caber above. The products I was looking at are https://www.carpet-underlay-shop.co.uk/products/thermo-pro-x-underfloor-heating-underlay-for-wood-or-laminate & https://www.everbuild.co.uk/products/adhesives/floor-adhesives/sika-silent-layer-mat/ this comes in 3mm and 5mm. Link to comment Share on other sites More sharing options...
SteamyTea Posted November 29, 2021 Share Posted November 29, 2021 (edited) 18 minutes ago, revelation said: https://www.everbuild.co.uk/products/adhesives/floor-adhesives/sika-silent-layer-mat/ this comes in 3mm and 5mm. They do not show the thermal conductivity, but it could be estimated from the data sheet. It has a density of 30-33 kg.m3 and is made from polyurethane. 18 minutes ago, revelation said: https://www.carpet-underlay-shop.co.uk/products/thermo-pro-x-underfloor-heating-underlay-for-wood-or-laminate This one has a Tog rating of 0.3 A Tog (comes from the word for clothing, Toga)1 TOG = 0.1 m2.K.W-2. So at 0.0018m thick 0.0018 [m] / 0.9 [ W.m-1.K-1] = 0.002 [R = m2.K.W-1] 1 / 0.002 [R] = 500 [U = W.m-2.K-1] It should really be called a thermal conductor, not an insulator, but it is very thin. Edited November 29, 2021 by SteamyTea Link to comment Share on other sites More sharing options...
Olf Posted November 29, 2021 Share Posted November 29, 2021 Nah, why overcomplicate again? Stated 0.3 tog => R = 0.03 m2K/W U=1/0.03=33 W/m²K Clearly the winner, the trick used of course is thickness of next to nothing - but if the floor surface permits, that is the way to go. Link to comment Share on other sites More sharing options...
revelation Posted November 30, 2021 Author Share Posted November 30, 2021 I think that is the one I will go with, we want it to conduct heat through easily rather than insulate. However we would like it to provide some sound proofing too. Link to comment Share on other sites More sharing options...