May 27, 20215 yr After a slight cock up (not mine thankfully) we have one external wall that will have to be narrower than the rest (long story...) Original proposal from outside was: render, 100mm block, 240mm EPS blown bead, 100mm block, plaster. For this one wall it will have to be narrower, so builder is suggesting: render, 100mm block, 115mm Kingspan K106, 100mm light weight block, plaster. From Kingspan brochure: Both are around about 0.13 W/mK. Just wondering if there are any clever ideas for alternatives that result in the same or better u value and no thicker?
May 28, 20215 yr For me,that system requires such attention to detail & supervision during the install that you don’t actually achieve the u-value they claim. Think about a bricky on the scaffold cutting those sheets at a tray damp detail,or around a lintol,or even just up to a cavity closer on a reveal. Trust me,there’ll be gaps galore.
May 28, 20215 yr Author Quote For me,that system requires such attention to detail & supervision during the install that you don’t actually achieve the u-value they claim. Think about a bricky on the scaffold cutting those sheets at a tray damp detail,or around a lintol,or even just up to a cavity closer on a reveal. Trust me,there’ll be gaps galore. Yes indeed, that was a large factor in the decision to go with the blown bead. Quote You could upgrade to the silver/graphite? blown in beads to get a better u value Already using silver...
May 28, 20215 yr What about insulated plasterboard? Basically another 50mm of PIR, and reduces any cold ridges through the cavity.