OldSpot Posted December 21, 2020 Share Posted December 21, 2020 I'm trying to find information on sizing to and from an UFH manifold. Does any one know of a source please? The run is approx. 12m and LoopCad says ~ 15l/min needed in total for the UFH loops. Many thanks. Link to comment Share on other sites More sharing options...
MikeGrahamT21 Posted December 21, 2020 Share Posted December 21, 2020 22mm minimum, will give you 36l/min. 15mm only just scrapes in at 18l/min Link to comment Share on other sites More sharing options...
OldSpot Posted December 30, 2020 Author Share Posted December 30, 2020 Cheers Mike Link to comment Share on other sites More sharing options...
PeterW Posted December 30, 2020 Share Posted December 30, 2020 Heat source ..? Buffer ..? Minimum 22mm, depending on the other items you may need 28mm Link to comment Share on other sites More sharing options...
OldSpot Posted December 30, 2020 Author Share Posted December 30, 2020 @PeterW Hi Peter, Heat source is an oil (system) boiler and I'm looking at whether/how to use a buffer as I'm concerned about the boiler cycling too much. On the issue of buffers.................I'm actually just going through that now. My current thinking is to use a 150/200l indirect tank to buffer (LoodCad suggests UFH is about 11kW, which correlates reasonably well with my heatloss calcs). It will only serve the UFH. I'm getting a little lost on whether the tank needs to be vented or can be sealed. The coil would be from the boiler but would the UFH side then be classified as unvented (due to tank size) and come under G3 if it was a sealed system? I could alternatively fit a small F&E tank directly above the tank if needed Link to comment Share on other sites More sharing options...
PeterW Posted December 30, 2020 Share Posted December 30, 2020 100 litre buffer will be fine - don’t bother with a coil, just make sure there is a mag filter on the way back to the boiler. Link to comment Share on other sites More sharing options...
OldSpot Posted January 1, 2021 Author Share Posted January 1, 2021 Thanks Peter, Any reason a simply stainless steel direct cylinder (like this) can't be fitted? Link to comment Share on other sites More sharing options...
PeterW Posted January 1, 2021 Share Posted January 1, 2021 Anything like that will do. 900x400 for £169 delivered here https://www.cylinders2go.co.uk/shop/vented-cylinders/direct-vented-copper-cylinders/900-x-400-direct-copper-cylinder/ Link to comment Share on other sites More sharing options...