December 4, 20205 yr Hi, I may be over thinking it but does anyone know for the potential of condensation on the extract and supply ducts with UFH pipes being in close proximity. I will likely be using galvanised steel spiral wound duct which will pass through a PS10 253mm posi-joist and attached to the underside of the 1st floor T and G will be the underfloor heating pipes in a spreader plate. I'm sure the designers of either of the systems will have a good idea but I'm just trying to keep on top of things and would appreciate peoples thoughts? Thanks!
December 4, 20205 yr Condensation is less likely at higher temperatures. So I would expect proximity to ufh pipes to make condensation in mhrv duct less likely.
December 4, 20205 yr Author If we were to run the ASHP in cooling mode in summer could that potentially cause a problem then?
December 4, 20205 yr Yes, you will definitely risk getting condensation on the ducts if you use it in cooling mode, this will drip off and stain the ceiling. Insulating the ducts will reduce but not eliminate the problem. Good design will negate the problem, ideally by designing out the need for air cooling.
December 4, 20205 yr Author Sorry, it wouldn’t be the MVHR that I would be cooling it would be the UFH to cool the floor, If that makes any difference. I think I’ll end up insulating the duct for piece of mind.
December 5, 20205 yr Need to be very careful running cooled water to make sure that the cooled water temperature stays above dew point temperature