Jump to content

Most Efficient Use of ASHP


J1mbo

Recommended Posts

1 hour ago, joe90 said:

generally warmer (more heat available in the air?) but was told the difference in night and day air temps did not affect efficiency. Was/is this correct?


it is per K not °C above zero so the difference between 4°C and 8°C for example isn’t 100% more it is the difference between 277°K and 281°K which is 1.5%... 

 

The key is load shifting and being able to “store” the heat. UFH is good at this, radiators and building fabric less so due to heat capacity of air vs heat capacity of concrete etc. 

  • Thanks 1
Link to comment
Share on other sites

3 hours ago, PeterW said:


it is per K not °C above zero so the difference between 4°C and 8°C for example isn’t 100% more it is the difference between 277°K and 281°K which is 1.5%... 

 

The key is load shifting and being able to “store” the heat. UFH is good at this, radiators and building fabric less so due to heat capacity of air vs heat capacity of concrete etc. 

 

Surely it would be relative to the evaporation temperature, e.g. about -40*C for R290 IIRC. So 44 and 48, or 10% in that case.

Link to comment
Share on other sites

4 minutes ago, J1mbo said:

 

Surely it would be relative to the evaporation temperature, e.g. about -40*C for R290 IIRC. So 44 and 48, or 10% in that case.

It is a combination of all the factors. It is why CoP is used, it is more useful as an overall measure.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...