Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
I believe the calculation shows that the bungalow will need 13,350kW to heat the place. But the total electricity used last year for the whole place was less than 12,000kW so is their heat demand calculation incorrect? -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
I have finally received the heat loss calculations for the 70m2 bungalow. apparently it is suggesting a 10kW heat pump but the installer is thinking an 8kW would be sufficient. he's suggested a Samsumg. I do recall being told that the flow temperature is important for efficiency and lifespan of the heat pump. I can see a flow temp of 53oC - is this something i should ask about? Comments gratefully received. We do need to get this installed soon as my elderly parents feel the cold and are already commenting on the place being cold in the mornings! (we do have a night storage heater that we can turn on till the new system is installed). heatpump-design-calculations.pdf heatpump-system-performance 7 ellesmere.pdf hotwater-design-calculations.pdf room-by-room-calculations.pdf room-by-room-emitters.pdf -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
It certainly seems the case that they can quote whatever they like. We'll just have to bite the bullet and get it installed before the weather gets colder. -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
Here's another possible example of Rip off Britian - we just had a quote for supplying a scaffolding tower to access the house roof verge and soffit for painting and repair. One tower either side of the garage with beams across the top - £1500 plus vat. Am I just out of touch for prices or is this silly money??? -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
The second quote I had was for £8500 for materials (this was the Steibel Eltron ashp and cylinder) and 33200 labour, plus the electrician costs to connect theconsumer unit to the rotary isolators. -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
The original company are coming tomorrow to do a heat loss assessment. They said it can take up to 4 hours. Will report back once I have it. -
Exterior ideas needed!!
TheMitchells replied to Bournbrook 's topic in New House & Self Build Design
I like the brick and wood! Why change it? -
Central heating system and Asbestos
TheMitchells replied to TheMitchells's topic in Other Heating Systems
It would be a swizz if they did insist on a new EPC as nothing has changed since the last one. -
Central heating system and Asbestos
TheMitchells replied to TheMitchells's topic in Other Heating Systems
Yes, it is nice to know. Another example is my EPC inspector. I had organised for a new EPC as one of the companies who are quoting for the ASHP said I'd need one, our old one was out of date. (I did not check myself - Doh!🤪) Yesterday the guy who was coming, rang to say that my EPC was valid till 2028! So no need for him to come. What a nice chap! -
Any one bought this yet? Sounds like it could be useful, particularly for someone like me, who knows only what we are told by the industry. https://www.amazon.co.uk/dp/B0D6WBGSRV?_encoding=UTF8&dib_tag=se&dib=eyJ2IjoiMSJ9.aYF2hlRd4NDGeaORD3YlgX2BwaGtVAai_6RILxUYdSapFuQCFknreE9l1gzLdMO6DKdN3ZCdv1areI1Pawtu8OT-F-u1LLCBYCbTjbq3j97Vt_yiRdrBbwtjjqCeC1mjYXMO3q3dWEQQtySXid0QaA.br7hTlYkRRQJq9lzjx5s_Tl-lCABWAjM-hKh5S8XoSI&qid=1718263790&sr=8-5&linkCode=sl1&tag=myhomefarm-21&linkId=f2d6239efb72c296a20c3c2d78a1f177&language=en_GB&ref_=as_li_ss_tl
-
Thought folks would be interested to read this. Copied from the Renewable Heating Hub 27 July 2024. In a significant development for the renewable heating sector, an industry insider has revealed to Renewable Heating Hub that a new heat pump standard is on the horizon. This forthcoming standard, being developed in collaboration with Flexi-Orb, is poised to compete directly with the existing Microgeneration Certification Scheme (MCS). According to the source, this initiative promises to address many of the shortcomings associated with the current standards, offering a more practical and user-friendly approach for customers, installers and manufacturers alike. Full details here. https://renewableheatinghub.co.uk/new-standard-set-to-revolutionise-heat-pump-installations-in-the-uk
-
Central heating system and Asbestos
TheMitchells replied to TheMitchells's topic in Other Heating Systems
Good news! Contacted a company who deals with Electricaire units and they were able to check their register. No asbestos! So we can go ahead and arrange for it to be removed. Phew. -
Short term fix needed. Any suggestions?
TheMitchells replied to TheMitchells's topic in Electrics - Other
it was a light pen. Similar to one of these. https://www.screwfix.com/p/fluke-non-contact-voltage-detector-pen-1000v-ac/85949?kpid=85949&cm_mmc=Google-_-Datafeed-_-Tools?kpid=KINASEKPID&cm_mmc=Google-_-TOKEN1-_-TOKEN2&gad_source=1&gclsrc=ds However, we think the problem may be solved. An electrician finally came today after booking him Wednesday last week. Once he had removed the front of the Off Peak circuit board, this is what he found. Not good! He has replaced the Main switch and cleaned up the cables going into it and is happy that it should all work now. Particularly as we know the power is coming on during the night. So it wasnt Octopus's meter after all. And, if the electrician who I asked to come at the very beginning (10th July) had come and taken a look, we could have saved ourselves 3 weeks of aggravation. But instead he told me to contact Octopus and the rest is history as they say! So fingers crossed it all works okay overnight. The RCBO next to the main switch is slightly damaged too, but that is for the central heating system which we are replacing next month, hopefully, so that will remain turned off till then. He did say he could replace it but for now it is turned off. -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
I'll ask him when I next speak to him.. And I guess if it more efficient, then I can make do with extra radiators. -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
yes, we have double glazing and they arent too bad. The chap did say the het pumps from Stiebel Eltron are more than others but he feels they are worth the expense. We dont have too much loft insulation at the moment, minimum required, i believe but we will add more as soon as it is all installed. All the pipework and stuff will across the loft and drop to the required location, so we can then add the extra insulation on top of it all. -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
Hmm, the chap wh came to look at the place today was very scathing of such a high HP. He said we'd be looking at a one around the 7 mark, taking the floor at less than 100 square meters and a basic rate of about 70 - not sure what the 70 was but he was looking at the windows/walls and giving a broad estimate. He also siad they onlyuse Steibel eltron who provide the whole system, so it all works well together and has space for expansion should we want to add ufh in the future. have to admit that i liked him - he's local and said straight off that if we went for him, it wouldnt get done till end of September ish. So just waiting to get quote from him now. I did give him all the window/doors sizes and floor plan and he asked me to get an up to date EPC. The current one was presumably done when we bought the place in 2018. CVC got back to me but the quote was far more than the first quote without any deetails from us. So they are out of the running. Fingers crossed that the second guy gives a reasonable quote. 🤞 -
Short term fix needed. Any suggestions?
TheMitchells replied to TheMitchells's topic in Electrics - Other
now we are very confused🤔. Hubby went over and stayed at the property, checking the Night suppy cable at various times. there was no power in the cable at 10pm nor 1.21am . However, when tested at 2.53am there was power! 😃 When fitted, the Octopus fitter said night period started at 1am. So thats strange it had not been on earlier. However, even stranger was around 9am when Mum rang to say they still had no hot water or heating - though we know the power was getting through at 2.53am. 😢 So is it a problem with the night circuit? We have someone coming on Monday to dead test. I am also going to ask him to connect the two units to the daytime supply and we'll just add timers where needed. Hubby came home at 3am so we dont know if it stayed on or turned straight off. I shall maybe stay there tonight and check it throughout the night. -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
the current windows do not have trickle vents and I would not want them in any replacements. we plan to add mvhr when we do the renovation in a couple of years. The bedroom windows front onto quite a busy road which for me means closed windows. My parents are both going deaf so its not a problem for them. I had planned to have the unit under the front bedroom window. But the company who gave the quote say the regs say it cannot go to the front of the building if it fronts a highway. however, looking at the regs, it says in the case of land, other than land within a conservation area or which is a World Heritage Site, the air source heat pump would be installed on a wall of a dwellinghouse or block of flats if— (i)that wall fronts a highway; and (ii)the air source heat pump would be installed on any part of that wall which is above the level of the ground floor storey. As ours will be on the ground, I read that under the front window would be acceptable. We are not planning ufh yet - thats for the renovation and then we'd have a utility room so hopefully the manifold would go in there? I believe there would be a buffer tank with the hwc. and that is all going into the cupboard in the centre of the bungalow, where the current heating system is. Once we get it removed. Still waiting for the 2 asbestos companies to reply to my enquiry. job for the morning - chase them up. -
Short term fix needed. Any suggestions?
TheMitchells replied to TheMitchells's topic in Electrics - Other
will get some photo's tomorrow of both consumer units and meter box so hopefully can see. Hubby seems to think there is no main switch/isolator in the meter cupboard. -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
Oh no - please dont confuse me any more - there are so many options already!😁🫤 -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
I dont have one. I am trying to use Jeremy's spreadsheet but there are bits I dont understand. Here is my attempt. But as we dont nhave an mvhr, that may spoil any results. Heat loss calculator.xlsx -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
Scarily, it looks like they use 10,000 kW per year for hot water and heating. 😬 They do like it hot! Hubby is asking why we cant just add the radiators and a simple gas combi boiler?? I guess the easy answer is that there isnt gas to the property and the supplier for their area is talking about installation 10-12 weeks after acceptance of the quote, which was £1200. Unless we are able to connect into the neighbours incoming pipe? But with the central warm air unit still working (just), we could manage for a few months, getting the radiators fitted so that as soon as the gas is connected, a combi boiler could be fitted. It goes agaisnt my principles to use gas/fossil fuel. But it would be easy to install and probablly the cheapest option. Urhghh! The bill below shows their day and night use. The only thing on the night meter is the heating (mostly off currently apart from a small night storage heater in the shower room, turned low) and the hot water heating. -
Short term fix needed. Any suggestions?
TheMitchells replied to TheMitchells's topic in Electrics - Other
Plan now is to get an electrician round to connect the night circuit to the day one, so the poor Smart Meter only has one supply to worry about. And we can add the time switches as suggested by Alan Ambrose. Best he can do is Monday though 😒. Will i need to get Octopus to turn anything off? Or can he do it with the supply still on? And if they need to turn off the supply, can they do it remotely or do they need to come at the same time? -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
One bath but not used very often - once a week? I looked at Octopus for a quote but it looks like you have to pay £500 for it, which is then deducted from the cost. The ufh install will come with the extension but thats not for a couple of years time. I'm looking for a simple heat loss calculator that i can use myself. I know jeremy had one. Will look for that. -
Quote for ashp - didnt expect that much!
TheMitchells replied to TheMitchells's topic in Air Source Heat Pumps (ASHP)
One more thing - is a 210 hot water cyinder normal? our current one is only 120l and that seems fine. There is only ever going to be two people living there. And we have an electric shower so that would not come from the cylinder.