Bpc ufh design!

Featured Replies

So, I asked(paid) bpc to do a design for us, thinking that it may be easier/quicker than me getting my head around loopcad. I even sent my filled version of Jeremy's heat loss spreadsheet as thought that may help. I also sent crib notes stating what we were looking for.

Suffice to say I'm not massively impressed but, could I get opinions on it please?

Standouts for me are;

  1. So many loops at 150mm centres

  2. Flow rate of 1.1!

  3. Surplus heat in every room from 147% up to 433%

Surely they can't have

BPC_BPCZ-1000001899_261124_Bpc.pdf

Quite why they have added a loop in the utility god only knows. I guess they don't count the dozen or so loops to the manifolds as having any impact. Same with the hall. 200mm centres would save loads of pipe, loops manifold and install cost. Wait for comments from others here who know far more than me and go back asking for amendments.

56 minutes ago, lizzieuk1 said:

So, I asked(paid) bpc to do a design for us, thinking that it may be easier/quicker than me getting my head around loopcad. I even sent my filled version of Jeremy's heat loss spreadsheet as thought that may help. I also sent crib notes stating what we were looking for.

Suffice to say I'm not massively impressed but, could I get opinions on it please?

Standouts for me are;

  1. So many loops at 150mm centres

  2. Flow rate of 1.1!

  3. Surplus heat in every room from 147% up to 433%

Surely they can't have

BPC_BPCZ-1000001899_261124_Bpc.pdf

It’s not hideous, no less rudimentary than every other one I’ve seen this and last year, and the ones before them.

I usually take these and adapt them on the fly, as per the last maybe dozen or so I’ve laid for MBC or MBC’s clients, it just needs some common sense.

Agree, utility loop is moot, but perhaps its safer to offer it as a zone than be asked why that room hasn’t been serviced; assume the designer worked on generic arrangement here eg the rest are insulated and would output / offer “less heat”.

Flow rates are low, but not a problem, these would be balanced and the pump set accordingly.

Just needs a few tweaks, but if you provided rudimentary spec / detail, you can’t expect anything more by return, really.

It looks a lot better than a couple of the free designs we were offered. Do their heat loss calcs roughly match what you calculated yourself?

I noticed they've set a design temp of 45c but presumably you'll run it lower?

You could ask what the heat outputs look like at 35, still very comfortable I'm sure and the design might look less over-spec'd then. I also think it would be reasonable enough (given it's a paid design) to ask whether a higher flow rate and wider spacing might work better, or why they didn't go that way? (E.g more even heat with narrower spacing)

1 hour ago, lizzieuk1 said:

I also sent crib notes stating what we were looking for

Different of course if they've just ignored these!

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.