Fancoil flow temperatures on a Heatpump?

Featured Replies

Hi all

Anybody here run Fan coils with their Heat pump?

I'm looking to install a fan coil to a heat pump for the purpose of size reduction compared to large radiators which I don't really have the space for. All the major brands marketing says they work great with heat pumps. However I'm confused on how they could work?

General advice is to run a heat pump on weather compensation, modulating flow temperatures etc. Looking on the Open heatpump monitor website shows that real life running data of many heat pumps are that many happily tick along at temps such as 27, 32, 34 degrees etc most of the winter season. Only ever getting up to the higher temperatures in the brief cold snaps.

Digging into fan coils it appears they all seem to have temperature probes on the inlets that only allow the fans to run when flow temperatures exceed 35 degrees. I think I found only one that was set to 32

So how do people realistically run fan coils on a weather compensated heat pump if the unit will only kick in on the very coldest days of the year? I know there might be a way to override and manually operate the fan but that seems like a bit of a pain to do on a regular basis. Considering how much these units cost.

My plan was to run the fan coil on an open loop system of UFH downstairs and a Fan coil in the loft room of a bungalow loft conversion.

Many thanks in advance for any advice or thoughts.

To size a fan coil you refer to the data sheets for a given flow temp and get the expected heat output. You match output to room heat loss.

Flow temp max is defined by the design you have above. So bigger fan coil can run lower flow temp for a given output. Smaller fan coil requires higher flow temp.

Min flow temperature, a temperature probe measures water flow temp and gives a permission for fan to operate. Cheap units this is a fixed flow temp, others you change the value in installer settings.

I would probably run a fixed flow temp of around 33-35 degs if you want the full flexibility of the fan coil sized correctly for the space. If you want WC on the UFH run a mixer driven by the ASHP.

My Ecovector units use the 35degrees. I have a proper ducted Daikin unit but haven’t found time to fit it yet. The ecovector is more a drop in Rad replacement with more capacity and noise. The Ducted unit requires a bit more design and control as per John above.

  • Author
On 17/11/2026 at 11:06, JohnMo said:

To size a fan coil you refer to the data sheets for a given flow temp and get the expected heat output. You match output to room heat loss.

Flow temp max is defined by the design you have above. So bigger fan coil can run lower flow temp for a given output. Smaller fan coil requires higher flow temp.

Min flow temperature, a temperature probe measures water flow temp and gives a permission for fan to operate. Cheap units this is a fixed flow temp, others you change the value in installer settings.

I would probably run a fixed flow temp of around 33-35 degs if you want the full flexibility of the fan coil sized correctly for the space. If you want WC on the UFH run a mixer driven by the ASHP.

Just been speaking to all the tech departments for the major UK Fan coil suppliers. Panasonic, Daikin, Myson all say it's not adjustable? Cool energy (Reverso) say not adjustable but they are looking to add this in the future when they update their firmware. Don't know when or even if this can be applied retrospectively. Mitsubishi told me that are withdrawing Fan coils from the UK market. But most of them do say unplugging the probe will just mean the fan runs all the time or off a room stat.

One of my problems is in order to comply with MCS for the Grant The emitter needs to meet the heat loss calculated by the installer. Which they have worked out as 960 watts. My own heat loss calculation makes it 600 watts. So I was going to size it based on heat output on full fan speed to keep the Installers MCS tick box happy. Then I can hopefully (if i've done my maths right) have my 600 watts output on the lowest fan speed.

Fixing the lowest flow temp I worry its going to ruin any efficiency through the shoulder seasons or lead to excess cycling of the heat pump?

It's probably not much help, but I've fitted a Thermix kickspace which will adjust down to 25c.

Thermix

Heat Pump Plinth Heaters - Thermix

1 hour ago, SteveG40 said:

Myson all say it's not adjustable?

That is simply incorrect, as it adjustable on iVectors, as I have one. You go into install settings and it can be adjusted for heating and cooling mode.

Looking at @LaChab link, if you look further they also do wall mounted fan coils https://kitchenheaters.co.uk/product/habanero-1-4kw-fan-convector-with-wireless-thermostat/

I have the cool energy reverse CE800 unit as well and it came without a controller so have a cheap Tuya job. It regulates 3 fan speeds depending on the temp set difference to temp in the space.. it has no intelligence of what temp the water entering or leaving is so I had to add some HA intelligence to only run when the water temp was X so that it didn’t circ cold air. It will depend on the controller you use but behaves more like a ‘proper’ FCU. (It is just a heat exchanger and a fan in a pretty box).

I run six water fan coils (Clivet Aura) on my heat pump, with the water at about 30 to 36 °C through the winter, and they heat fine at that. On weather compensation a fan coil behaves like any other emitter: as it gets milder the water gets cooler and the unit gives less, but the room needs less too. The only thing in the way is that cut-in probe. So rather than fixing the flow temperature at 33-35 °C, I'd pick a unit where the cut-in can be set lower (JohnMo's iVector, LaChab's Thermix down to 25 °C) or, as the suppliers told you, unplug the probe and let a room stat run the fan. A fixed 35 °C in mild weather is what would cost you efficiency and make the heat pump cycle.

On an open loop the underfloor decides the water temperature and the fan coil gets that same water. So, like JohnMo said, match the datasheet output to the room, but read it at your underfloor's design flow temperature, not the headline figure. Most datasheets rate at 45/40 °C. At 35/30 °C the water is 12.5 °C above a 20 °C room instead of 22.5 °C, so expect a bit over half the catalogue output: for the installer's 960 W on top speed you'd want a unit of about 1.7 kW at 45/40.

Sizing for 960 W on top speed and living on low speed for your 600 W is a good plan, it's quieter too. I'd still ask the installer for that room's line of the calculation: a gap that size is usually the air changes or the room temperature they assumed. I did mine room by room as well, fan coils included [commercial link removed]. For a loft room, if your heat pump can cool, the same unit cools it in summer. It then needs a condensate drain and insulation on the pipes to it.

Edited by jack
Commercial link removed.

  • Author
On 19/11/2026 at 12:27, JohnMo said:

That is simply incorrect, as it adjustable on iVectors, as I have one. You go into install settings and it can be adjusted for heating and cooling mode.

Looking at @LaChab link, if you look further they also do wall mounted fan coils https://kitchenheaters.co.uk/product/habanero-1-4kw-fan-convector-with-wireless-thermostat/

Thanks for the Info John, So in the menu setting you can actually reduce the Fan cut off limits that the temperature probe uses? So you can reduce it down to say perhaps down to 25 degrees allowing the Fan to run regardless of what temperature the Heat pump kicks out? To be honest the chap I spoke to from Myson did send me a follow up email and his title in his email signature did state 'Apprentice Design Project Coordinator'

  • Author
On 19/11/2026 at 15:05, Wil said:

I have the cool energy reverse CE800 unit as well and it came without a controller so have a cheap Tuya job. It regulates 3 fan speeds depending on the temp set difference to temp in the space.. it has no intelligence of what temp the water entering or leaving is so I had to add some HA intelligence to only run when the water temp was X so that it didn’t circ cold air. It will depend on the controller you use but behaves more like a ‘proper’ FCU. (It is just a heat exchanger and a fan in a pretty box).

I did look at the Reverso units. I quite like them visually, and many of the others look a little bit like Night storage heaters. The Reversos look a bit better Have you been happy with the build quality of it?

3 minutes ago, SteveG40 said:

So you can reduce it down to say perhaps down to 25 degrees allowing the Fan to run regardless of what temperature the Heat pump kicks out?

You can but it's not really the best way to operate as it just starts blowing room ambient temperature about, so it's just drafty. You want the fan to stop if the heat pump cycles off, unless you are pumping from a large buffer tank.

Copy of settings page from manual. CSP and HSP are the settings.IMG20261125161105.jpg

  • Author
15 minutes ago, JohnMo said:

You can but it's not really the best way to operate as it just starts blowing room ambient temperature about, so it's just drafty. You want the fan to stop if the heat pump cycles off, unless you are pumping from a large buffer tank.

Copy of settings page from manual. CSP and HSP are the settings.IMG20261125161105.jpg

Perfect! Thanks again John. Does clearly state there its adjustable. So it's 32 degrees by default and I'm guessing it can be reduced to a lower setting rather than 32 and can be adjusted up only? Regarding it feeling drafty, I believe this might be the reason many of these units have this fan cut out probe. Body temperature being 36 odd degrees and airflow that is below that to a certain point will feel like a cold draft despite the airflow actually being higher that room temperature. Probably something we'll have a fiddle about with once it's all fitted and running. But ideally if I can get a unit where this is adjustable out the box than at least i've got the option.

38 minutes ago, SteveG40 said:

I did look at the Reverso units. I quite like them visually, and many of the others look a little bit like Night storage heaters. The Reversos look a bit better Have you been happy with the build quality of it?

I had to adjust the fan as it was imbalanced and running noisily. Since then it’s been. Fine. I’ve tried it horizontally and vertically (much better). For the permanent solution I’m hiding a ducted unit in the loft. I’ll re-use the reverse somewhere where the fan noise is less impactful (currently in the living room).

  • Author
On 20/11/2026 at 07:11, gac said:

I run six water fan coils (Clivet Aura) on my heat pump, with the water at about 30 to 36 °C through the winter, and they heat fine at that. On weather compensation a fan coil behaves like any other emitter: as it gets milder the water gets cooler and the unit gives less, but the room needs less too. The only thing in the way is that cut-in probe. So rather than fixing the flow temperature at 33-35 °C, I'd pick a unit where the cut-in can be set lower (JohnMo's iVector, LaChab's Thermix down to 25 °C) or, as the suppliers told you, unplug the probe and let a room stat run the fan. A fixed 35 °C in mild weather is what would cost you efficiency and make the heat pump cycle.

On an open loop the underfloor decides the water temperature and the fan coil gets that same water. So, like JohnMo said, match the datasheet output to the room, but read it at your underfloor's design flow temperature, not the headline figure. Most datasheets rate at 45/40 °C. At 35/30 °C the water is 12.5 °C above a 20 °C room instead of 22.5 °C, so expect a bit over half the catalogue output: for the installer's 960 W on top speed you'd want a unit of about 1.7 kW at 45/40.

Sizing for 960 W on top speed and living on low speed for your 600 W is a good plan, it's quieter too. I'd still ask the installer for that room's line of the calculation: a gap that size is usually the air changes or the room temperature they assumed. I did mine room by room as well, fan coils included [commercial link removed]. For a loft room, if your heat pump can cool, the same unit cools it in summer. It then needs a condensate drain and insulation on the pipes to it.

Many thanks gac, useful advice thank you. I have been looking at units that are higher outputs for this reason. I can see exactly where the installer got his calcs to get that figure. Firstly he used the Heat Engineer software. I can see they have presets for complex room shapes for loft conversions, vaulted ceilings etc. He selected the pitched gable ended option as it was the closest available. Our room is actually pitched and hipped so I actually have less room volume that he worked out. Windows auto filled as standard Double glazing 2.1 U value and we are going triple glazed. He also calculated the attached Ensuite with the older Cibse guidance air change of 2 or 3 but our extractor outlet is going straight into the MVHR and we are upping the airtightness because of the MVHR. If I put the basic figures his software used into my home made spreadsheet I actually get his result. Which helped me feel confident in my spreadsheet skills :-). I decided not to correct him as the heat pump decided on is a 5KW. If I got him to edit the calcs I risk ending up with having the 3.5kw version and I would rather stick with the 5kw for DHW recharging and a little more headroom if the weather gets real cold in some freak beast from the east style situation. Plus the 3.5kw and the 5kw I believe have the same minimal modulation anyway.

I'm looking at the units with the condense collection tray the room directly below is a bathroom with a handy soil stock to tap into and we'll be wrapping the pipes up tight. I know the common weak spots when It comes to condensation! In my day job I'm a delivery engineer for baby super yachts, many have fan coils for heating and cooling running off effectively an 'Ocean source' heap pump. When we have the air con chillers running at 6-7 degrees in the height of summer you get to see the weak spots dripping all over the place! exposed valve handles and at points where the insulation has not quite made it to the area above the drip trays are common places.

  • Author
57 minutes ago, Wil said:

I had to adjust the fan as it was imbalanced and running noisily. Since then it’s been. Fine. I’ve tried it horizontally and vertically (much better). For the permanent solution I’m hiding a ducted unit in the loft. I’ll re-use the reverse somewhere where the fan noise is less impactful (currently in the living room).

I did/am considering a ducted unit. It's something I'm looking at adding in the future and prepping for it with pipe sizes. But for now the HP installer just wanted to see a simple wall mounted unit with output to match for his MCS tick box list and so we can get the BUS grant, It been a bit of a stretch to get him on board with a Fan coil, he wanted me to install standard radiators. Once it's all installed and MCS signed off AND i've finished the rest of the house!! then I can turn to tinkering and playing around with stuff.

Create an account or sign in to comment

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.