I'm looking at replacing a couple of rads with fan coils for when we get a heat pump installed in November.
Our plan is fully open loop system with UFH downstairs and rads / fan coils upstairs. Heat loss suggests the highest flow temp I will need is ~35 degrees c and plan to modulate flow based weather comp.
However, it seems like fan coils (Panasonic and Cool Energy Reverso) have a min flow temp of 35 degrees to turn on. Can't get a straight answer from manufacturers if that's when using the fan coil thermostat, or if it can be manually overridden to just run the fans on low no matter the incoming water flow temp.
Anyone got any experience or advice?
Get the manual downloaded, many have adjustable temps for cooling and heating. Don't ask read the installer manual. We have a Myson iVector MkII, it allows for adjustment of the flow temp to start stop the fan.
You can manually put fan on a fixed speed but then you don't get a modulating output.
Unfortunately the Reverso manual (installer) has no reference to this temperature and was only able to get the info from the manufacturer.
Re the Myson you have the installer manual says the fans won't turn on in heating mode unless the flow is 30degrees C. Is this true?
*Edit your manual looks like it cracks on if it doesn't detect a flow temp probe.
Edited by mistake_not
No, the 30 Deg figure is adjustable you can also run fan in manual so it runs 24/7 if you want. Our flue temp in heating is about 28 at most. So mine comes on about 24 for heating and about 18 for cooling
Screenshot_2026-08-08-20-23-23-63_40deb401b9ffe8e1df2f1cc5ba480b12.thumb.jpg.b8a70aba2a7efb75d1a4bf72d44826ab.jpg